Thread: I/O type for Instrument Index

  1. I/O type for Instrument Index

    Is the I/O type for the below correct?

    1. Motor Operated Valve (MOV)

    Tag Number Loop Instrument Type I/O type System
    MOV-001 M-001 Motor Operated Valve - -
    HS-001 M-001 MOV Local/Off/Remote DI SIS
    ZA-001 M-001 MOV Battery low alarm DI PCS
    ZSC-001 M-001 MOV Limit switch close DI SIS
    ZSO-001 M-001 MOV Limit switch open DI SIS
    HSX-001 M-001 MOV Local Handswitch - -



    2. VFD

    Tag Number Loop Instrument Type I/O type
    HS-001 V-001 HOA Switch DI
    XC-001 V-001 Pump Start DO
    XS-001 V-001 Pump Run Status DI
    XY-001 V-001 Permissive DI

    What is the I/O for Accelerometer?

  2. # ADS
    Spons Circuit
    Join Date
    Always
    Posts
    Many
     
  3. Re: I/O type for Instrument Index

    Attached are the typicals for the MOV and VFD. Is the I/O type correct? Is that enough information for the Control system vendor or do I have to include anymore?

    MOV

    [link Point to another website Only the registered members can access] Tag Number Loop Instrument Type I/O type System
    MOV-001 M-001 Motor Operated Valve - -
    HS-001 M-001 MOV Local/Off/Remote DI SIS
    ZA-001 M-001 MOV Battery low alarm DI PCS
    ZSC-001 M-001 MOV Limit switch close DI SIS
    ZSO-001 M-001 MOV Limit switch open DI SIS
    HSX-001 M-001 MOV Local Handswitch - -

    VFD

    [link Point to another website Only the registered members can access] Tag Number Loop Instrument Type I/O type
    HS-001 V-001 HOA Switch DI
    XC-001 V-001 Pump Start DO
    XS-001 V-001 Pump Run Status DI
    XY-001 V-001 Permissive DI
    What is the I/O for Accelerometer?


  4.    Sponsored Links



    -

  5. #3

    Join Date
    Sep 2008
    Location
    Here only- EGPET
    Posts
    699
    Blog Entries
    5

    Re: I/O type for Instrument Index

    if not connected with Bently system ( proprietary system) you can ask vendor to provide 4- to 20 mA i*e Analog input.

  6. #4

    Re: I/O type for Instrument Index

    Why the following signals send to SIS instead of PCS?
    HS-001 M-001 MOV Local/Off/Remote DI SIS
    ZSC-001 M-001 MOV Limit switch close DI SIS
    ZSO-001 M-001 MOV Limit switch open DI SIS

    I understood that signal sends to SIS shall be for trip and shutdown functions. Pls. correct if I'm wrong.

    Rgds*

  7. Re: I/O type for Instrument Index

    VT - Velocity Transmitter (AI)
    VI - Velocity Indication (Soft indicator)

    Check your projects Engineering Tag Numbering System first.

  8.    Spons.


  •   

Similar Threads

  1. The Mond Index
    By DORIO in forum Safety And Environment
    Replies: 0
    Last Post: 07-02-2015, 09:20 AM
  2. Steel Index Prices
    By aadamx in forum General Engineering
    Replies: 3
    Last Post: 01-16-2012, 05:52 PM
  3. Replies: 3
    Last Post: 08-05-2010, 10:44 PM
  4. the mond index
    By davide7 in forum Safety And Environment
    Replies: 0
    Last Post: 08-01-2010, 03:41 PM
  5. productivity index
    By karim ramadan in forum Reservoir
    Replies: 2
    Last Post: 02-06-2010, 12:18 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •