Thread: Devices is located in zone 1, Gas Group IIA/IIB T3

  1. Devices is located in zone 1, Gas Group IIA/IIB T3

    Dear All

    we have some electrial devices will be located at Zone 1 Gas Group IIA/IIB T3, the device will be mounted inside a JB EEX'de' so What kinds of certificate will be suit for the electrical devices?

    Thanks and best regards!
    Last edited by maiduyson; 12-17-2010 at 07:23 AM.

  2. # ADS
    Spons Circuit
    Join Date
    Always
    Posts
    Many
     
  3. dear maiduyson
    electrical devices for use in hazardous area and manufactured within European Community must be "Ex" marked as well as provided with a Notified Body certificate.

    Similar regulation exist worldwide with differences among countries; contact the local authority for details.

    I can attach here a poster for a brief clarifications of what EC and USA use.
    Attached Files Attached Files