  1. Thumbs up Help - Difference Between Two Level Transmitters (DP diaphragm seal)

    Dear*

    I am having problems with level measurement in a vessel.
    In this vessel* we have 2 level transmitters (one for safety and one for control) and both are DP transmitter with diaphragm seal.

    Those transmitters are connected in different process connection* being them:
    - Control Level transmitter connected directly to the vessel.
    - Safety Level transmitter connected in a StandPipe (Bridle)

    The superior and inferior connections of both transmitter have the same elevation* in other words* they supposed to have the same level indication.

    ENGINEERING DATA:

    The specification of the transmitters are:
    - Dp cell Transmitter + Diaphragm seal.
    - Process connection 2" FLG 600# RJT + Flushing Ring
    - Capillary fluid: Syltherm XLT (0*85 SG)
    - Control Transmitter: Foundation Fieldbus (Rousemount 3051CD2F22A1AS2M5B4E2Q4 + 199DAB59 AFCWG4DAA9H)
    - Safety Transmitter: Conventional 4-20mA (3051CD2A22A1AS2M5B4E2Q4 + 1199DAB59 AFCWG4DAA9H)

    Our vessel (vapor-liquid separator vessel) receive a stream of Natural Gas (GAS IN) and operates with 3 phases:
    - G&#225;s (lighter Hydrocarbon components). - GAS OUT
    - Liquid HC (Heavier Hydrocarbon components). - OIL OUT
    - Glycol + Water - WATER OUT

    Vessel operation conditions:
    - Pressure: 39*5 kgf/cm2G
    - Temperature: -28 Celsius Degrees (Below zero temperature).
    - Gas Density: 43*31 kg/m3
    - Liquid HC Density: 530*00 kg/m3
    - Glycol+Water Density: 1074*2 kg/m3

    Boths instruments are installed to measure the LIQUID HC phase (SG 0*53).
    - Distance between Superior and Inferior Level Connections: 1000mm
    Range: -850mmh20 to -320mmh20. (0% and 100% - without gas weight compensation)

    The vessel and the standpipe have insulation.

    [link Point to another website Only the registered members can access]

    [link Point to another website Only the registered members can access]

    MEASUREMENT PROBLEM:

    Although the transmitters are equal and have the same elevation in their process connection* they present different percentage level indication:

    [link Point to another website Only the registered members can access]

    The instrument that is connected to the standpipe (Control – Blue line) always show its indication below the instrument that is connected directly to the vessel (Safety - Green Line).

    MY HYPOTHESIS:

    1) Calibration mistake

    Once they have a different system (Foundation Fieldbus and 4-20mA) maybe occurred any mistake in calibration process (range selection and parametrization).
    I saw the configuration and both have the same calibrated range (-850mmH20 to -320mmH20).

    Any of you can see any calibration mistake can cause this kind of error between this transmitters?
    Can some AI block parameter cause this difference?


    2) Measurement Difference Cause by Process (StandPipe x Vessel)

    After I went to the field I started to think that this error could be caused by a Convection Flow between the standpipe and the vessel.

    If the standpipe has a higher temperature* can it cause the difference between the transmitters?

    As they are DP transmitters* I think just density variation (static analysis) does not explain the difference between them* once they are calibrated with same range.

    The Standpipe has a Magnetic indicator (304L body - not insulated) and seemed to be at a hotter temperature than the vessel. I used a pyrometer and the temperature of the Magnetic Indicator surface was 20 Celsius Degrees (positive and have way more temperature than -28 degrees of the vessel).

    Once the magnetic indicator is not insulated* Could it induce error caused by excessive heat transfer? Can it make the temperature in standpipe hotter than the vessel?


    Can the evaporation in the standpipe be causing a flow due to the convection phenomenon?


    If yes* I think it causes a different pressure in both transmitters. See figure below.

    [link Point to another website Only the registered members can access]

    Thank you very much for your attention.

    If you need any more information* please ph.prado@gmail.com or SKYPE: pedrohenriquesousaprado
    I have some prints of the configuration.


    Best Regards*
    Pedro H. S. Prado


  2. # ADS
    Spons Circuit
    Join Date
    Always
    Posts
    Many
     
  3. #2

    Re: Help - Difference Between Two Level Transmitters (DP diaphragm seal)

    Hi,

    First of all, it is the safety level transmitter who should be connected directly to the vessel.

    Second, it looks like you have a zero offset in one of the transmitters, you may want to proceed with zero adjustment.

    good luck.

  4.    Sponsored Links



    -

  5. Re: Help - Difference Between Two Level Transmitters (DP diaphragm seal)

    Interesting that you provide a lot of good information, but you do not reveal a set of comparison readings so that the magnitude of the error can be assessed. Why is the differences in readings always kept a secret?

    >"As they are DP transmitters* I think just density variation (static analysis) does not explain the difference between them* once they are calibrated with same range."

    DP is always ALWAYS, always density/specfic gravity dependent. DP reports in units of water column. The conversion to level is ALWAYS density dependent. Any difference in density from the design density (the value used for determining the physical level vs the units water column DP reading) is a proportional error. Always. It cannot be avoided when using hydrostatic pressure as the measurement.

    I suspect that the difference in density between the cooler vessel and the hotter bypass allows a thermal convection flow between the vessel and the bypass through the lower bypass connection, resulting in two containers (one the vessel, the other the bypass) each with its own density that differs from the other container's density resulting in two different reported levels.

  •   

Similar Threads

  1. The difference between ASTM A 578 Level II and Level B
    By minhky032003 in forum Materials Science &Corrosion
    Replies: 0
    Last Post: 08-28-2013, 10:09 AM
  2. Standard for designing displacer type level transmitters
    By f_nosferatu in forum Instrumentation & Control
    Replies: 0
    Last Post: 07-06-2013, 09:59 AM
  3. Details on diaphragm pumps
    By ayush842001 in forum Mechanical Engineering
    Replies: 0
    Last Post: 08-08-2012, 08:15 PM
  4. Article: Level transmitters discrepancy
    By Sabeur in forum Home Articles
    Replies: 2
    Last Post: 02-09-2011, 08:49 AM
  5. Level transmitters discrepancy
    By Sabeur in forum Instrumentation & Control
    Replies: 3
    Last Post: 01-25-2011, 06:05 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •