    Question API 650 - Floating roofs - Emergency roof drains

    Refererring to API 650 - Para. C.3.8.2 Emergency Roof Drains. The following is stated:

    "Double-deck roofs shall have a minimum of three open-ended emergency roof drains designed to provide drainage to prevent
    sinking the roof during severe rainfall events. Emergency drains are prohibited on single-deck floating roofs. Elevation of the
    emergency overflow drains shall be such that the outer rim cannot be completely submerged. These drains shall discharge at
    least 300 mm (1 ft) below the bottom of the roof and shall consist of open-ended pipes, braced as necessary to the roof structure.
    The drains shall be sized to handle the rainfall specified by the Purchaser, with a minimum diameter of NPS 4. The drains
    shall be sealed with a slit fabric seal or similar device that covers at least 90% of the opening that will reduce the productexposed
    surfaces while permitting rainwater passage. The drains shall be fabricated from Schedule 80 pipe, or heavier, and fittings
    with 6 mm (1/4-in.) thick roof deck reinforcing plates."


    Can anyone kindly provide me with a reason as to why emergency roof drains are prohibited on single deck floating roofs?

  2. # ADS
    Spons Circuit
    Join Date
    Always
    Posts
    Many
     
  3. #2

    Re: API 650 - Floating roofs - Emergency roof drains

    Central decks of Double Deck roofs are very stiff and do not deflect. In case of single deck the flexible central deck membrane deflects under the rainwater load. This could cause backflow of contents on to the roof if the head over the emergency drain is less than upward thrust of contents in deflected shape.

    Regards,

  4.    Sponsored Links



    -

  5. #3

    Re: API 650 - Floating roofs - Emergency roof drains

    Central decks of Double Deck roofs are very stiff and do not deflect. In case of single deck the flexible central deck membrane deflects under the rainwater load. This could cause backflow of contents on to the roof if the head over the emergency drain is less than upward thrust of contents in deflected shape.

    Regards,

Similar Threads

  1. Floating roof oil tank drawing
    By A.Venugopal in forum Mechanical Engineering
    Replies: 9
    Last Post: 07-07-2018, 04:35 PM
  2. floating roof calculation
    By soltane72 in forum Reservoir
    Replies: 19
    Last Post: 07-07-2018, 04:32 PM
  3. Design of stilling wells for floating roofs
    By adamjin in forum Mechanical Engineering
    Replies: 0
    Last Post: 08-06-2014, 10:16 AM
  4. External floating roof
    By DesEng in forum Mechanical Engineering
    Replies: 0
    Last Post: 01-10-2014, 09:37 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40