    Power cable

    Hi All,

    3x 1C cable lay above the ground from substation to substation, 1 week after commission it was found the tray is over heating. what is the cause of the tray over heating, this single core was lay apart.

    please advise.

    Regards
    Cy

  2. # ADS
    Spons Circuit
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many
     
  3. #2
    Is likely to be due to eddy currents

    But explain best the phenomena with a drawing, were are indicate the dimensions and distances, cable type (armour, unarmour) voltage, current, path length, etc.
    The cable is in trefoil or laid in flating formation (separate or touching)?

    the formulas to understand the problem can be found in IEC 60287

    bye

  4.    Sponsored Links



    -

  5. #3

    Join Date
    Dec 2009
    Location
    Riau, Indonesia
    Posts
    177
    Wel, overheating means energy, try to look for the energy source, such as :
    1. Electro magnet looping from metal cable ties that forming CT.
    2. single core cable lays in different tray.
    3. ground current from ground "summing" flows through tray to ground
    4. Both ground end of cable is grounded so the cable is heated up
    5. etc.
    But since you mention "single core lay apart", I suppose the magnetic and capacitance is not balance and transfered to tray. Try to implement "INTERPOSING" method.
    Hope this will help you.

  6. #4

    Join Date
    Feb 2011
    Location
    saudi arabia
    Posts
    210
    Hi All,

    This cable is single core connected to main substation to sub substation from 22kv to 6.6kv, distance between 1c cable is 300to400mm.

    Regards
    Cy

  7. Quote Originally Posted by cytech View Post
    Hi All,

    This cable is single core connected to main substation to sub substation from 22kv to 6.6kv, distance between 1c cable is 300to400mm.

    Regards
    Cy
    Clear answer. You cannot lay powercables single core segregated.
    Trefoil installation with cleats for dynamic forces is the only solution.

  8.    Spons.


  9. #6

    Red face ^^

    Please check list :
    1. Connection all point.
    2. Current in grounding. <<< The most of problem.
    3. However , if Temperature are not anymore from cable data sheet specification, you 're not serious.

Similar Threads

  1. Power and Instrument Cable
    By cytech in forum Electrical & Power Engineering
    Replies: 2
    Last Post: 03-25-2012, 12:26 PM
  2. Cable szing small power (Instrumentation)
    By instsuresh in forum Instrumentation & Control
    Replies: 1
    Last Post: 10-15-2011, 01:42 PM
  3. Cathodic cable
    By cytech in forum Materials Science &Corrosion
    Replies: 0
    Last Post: 05-19-2011, 03:58 PM
  4. cable route
    By Alex_1986 in forum Instrumentation & Control
    Replies: 0
    Last Post: 12-08-2010, 09:23 AM
  5. Contactor Drop off Problem in Long Distance control Cable. cable capacitance
    By raj151857 in forum Electrical & Power Engineering
    Replies: 1
    Last Post: 10-29-2010, 05:38 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40