The short circuit calculation in 13.2kv is around 0.6KA, where it should be at least 16 kA, do any of you have any idea what may be happening?
The trasnformes ir Delta/Delta
This is the system:
Bus 1 - Bus 2 (Transmision line 33 kV) 1/0 ALUMINIUM 274 meters
Bus 3 - Bus 4 (underground network 33 kV) 1/0 ALUMINIUM 42 meters
Bus 4 - Bus 6 (Transmision line 33 kV) 1/0 ALUMINIUM 196 meters
-------------------------------------------------------------------------------------------------->
Bus 6 - Bus 7 ( 1MVA - 33/13.2 kV - Delta/Delta)
Bus 7 - Bus 8 (underground network 13.2 kV) 4/0 CU 400 meters
LOAD = 1.5 MVA
in Attachments there are the archives jpg and .rar of etap.
thanks.
![]()