  1. Question Problem with short circuit level in 13.2 kV in etap

    The short circuit calculation in 13.2kv is around 0.6KA, where it should be at least 16 kA, do any of you have any idea what may be happening?
    The trasnformes ir Delta/Delta

    This is the system:

    Bus 1 - Bus 2 (Transmision line 33 kV) 1/0 ALUMINIUM 274 meters
    Bus 3 - Bus 4 (underground network 33 kV) 1/0 ALUMINIUM 42 meters
    Bus 4 - Bus 6 (Transmision line 33 kV) 1/0 ALUMINIUM 196 meters
    -------------------------------------------------------------------------------------------------->
    Bus 6 - Bus 7 ( 1MVA - 33/13.2 kV - Delta/Delta)
    Bus 7 - Bus 8 (underground network 13.2 kV) 4/0 CU 400 meters
    LOAD = 1.5 MVA

    in Attachments there are the archives jpg and .rar of etap.

    thanks.

    Attached Images Attached Images
    Attached Files Attached Files

  2. # ADS
    Spons Circuit
    Join Date
    Always
    Posts
    Many
     
  3. #2

    Re: Problem with short circuit level in 13.2 kV in etap

    check it by hand calculations, on the source, check the kA level for 3Phase and 1phase SC currents.

    take that current and apply by hand the transformer ratio and get the SC fault level in the secondary, and check where your error could be. also check the fabriaction standar at transformer, IEC or ansi

  4.    Sponsored Links



    -

  5. Re: Problem with short circuit level in 13.2 kV in etap

    Thanks, I will do what you suggest

  6. Re: Problem with short circuit level in 13.2 kV in etap

    verify the data of transformer and specially the short circuit impedance Ucc

  7. Re: Problem with short circuit level in 13.2 kV in etap

    When in the transformer, I put Ucc = 0.001%, I increase the short circuit currents in 13.2 kV to 12 KA, but it is not logical that value, the typical value for that transformer is 6%

    [link Point to another website Only the registered members can access]

    Last edited by ingenieria12345; 09-11-2018 at 11:48 PM. Reason: correction

  8.    Spons.


  9. #6

    Re: Problem with short circuit level in 13.2 kV in etap

    Transformer is too small for that voltage level
    Maximum Let Through = Isc = (Transformer kVA) × 100 / ((√3)×(Secondary kV)×(%Z transformer))
    = 1000 x 100 / ((√3)×(13.2)×(6) = 0.729 kA.

  10. Re: Problem with short circuit level in 13.2 kV in etap

    the best verification is to calculate the Icc by classical method (Hand), and after verify all DATA of the network also the base of ( power and voltage) used in the software to calculate.

  11. #8

    Re: Problem with short circuit level in 13.2 kV in etap

    You have 1.5 MVA load and a 1 MVA transformer

    A 1 MVA transformer full load current at 13.2 kV = 43 Amps

    A 1 MVA transformer @ Z = 7.1% will give you around 600A short circuit current

    Solution:
    Increase MVA size of transformer or lower Z%

  •   

Similar Threads

  1. IEC Collection 070/150: IEC TC 73-Short-Circuit Currents
    By BornToSin in forum Mechanical Engineering
    Replies: 1
    Last Post: 11-25-2017, 05:58 AM
  2. Article: MVA Short Circuit from ETAP
    By Nald in forum Home Articles
    Replies: 1
    Last Post: 01-10-2013, 11:54 PM
  3. MVA Short Circuit from ETAP
    By Nald in forum Electrical & Power Engineering
    Replies: 4
    Last Post: 01-02-2013, 11:35 PM
  4. MVA Short Circuit from ETAP
    By Nald in forum Electrical & Power Engineering
    Replies: 0
    Last Post: 12-28-2012, 06:24 PM
  5. Short circuit KVA calculation.
    By Tarique Latif Jarwar in forum Electrical & Power Engineering
    Replies: 3
    Last Post: 12-25-2012, 10:43 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •