  1. #1

    MVA Short Circuit from ETAP

    Hi.

    As per one example in ETAP, Utility Information is given below

    MVA 3phase is 1500 MVA
    KV L-L is 34.5kV
    Current Short Circuit is 25.1kA
    computed as MVA 3phase / (1.732*kV L-L)

    for this one I have no problem. The problem that confuse me is the MVA L-G, as per data given below

    MVA 1phase is 1640 MVA
    Current Short Circuit is 27.4kA
    computed as MVA 1phase / (1.732*kV L-L)

    Now the question is as follows:
    1. How come that the MVA 1phase is 1640 MVA? MVA 1phase is just MVA 3phase /3 and suppose to be 1500/3 = 500 MVA.
    2. Why is the formula for single phase short circuit above has sq rt of 3 (this is for 3 phase only)?

    Hope you could help me

  2. # ADS
    Spons Circuit
    Join Date
    Always
    Posts
    Many
     
  3. Re: MVA Short Circuit from ETAP

    Is this from ETAP example ? Take it just as a example, like any data.
    If they are from vendor.clarify with them (also with us ;-) )

    The formula for single phase is wrong.

  4.    Sponsored Links



    -

  5. #3

    Re: MVA Short Circuit from ETAP

    Yes this is an Etap example. You mean the formula use by etap to calculate the short ckt for 1 phase is not correct? then why did engineers approved it in the first place? etap was been use in many years now with the same formula for 1 phase,

  6. #4

    Re: MVA Short Circuit from ETAP

    Hi,

    The values are correct. Getting the MVA short circuit whether in 3phase, single-to-ground, line-line, or double-line-to ground fault are calculated the same. Never forget that you are calculating the MVA in a three phase system, which is:

    MVA(3phase) = sqrt(3) * current * line-line voltage

    or

    MVA(3phase) = 3*current*line-ground voltage


    In my opinion, you are wrong in taking the idea of MVA(1phase) as a single phase. But, in ETAP, MVA(1phase) for GRID/UTILITY means the MVA(3phase) during a single line-to-ground fault.

    We can also think of it like this, "Why would there be single phase if the Grid is three phase?". Get what I mean?

    Check out the user guide of ETAP, I bet that you haven't read it. Go to section Power GRID and it reads like this:

    MVAsc
    Specify the short-circuit MVA for three-phase and single-phase (line-to-ground) faults.


    Hope it helps. Please ask me if you do have other questions.

    God bless!!

  7. Re: MVA Short Circuit from ETAP

    Nald,
    I said the formula "computed as MVA 1phase / (1.732*kV L-L)" is wrong.
    It shall be MVA 1phase / (kV* L-G) .

  8.    Spons.


Similar Threads

  1. Article: MVA Short Circuit from ETAP
    By Nald in forum Home Articles
    Replies: 1
    Last Post: 01-10-2013, 11:54 PM
  2. MVA Short Circuit from ETAP
    By Nald in forum Electrical & Power Engineering
    Replies: 0
    Last Post: 12-28-2012, 06:24 PM
  3. Short circuit KVA calculation.
    By Tarique Latif Jarwar in forum Electrical & Power Engineering
    Replies: 3
    Last Post: 12-25-2012, 10:43 PM
  4. Short-circuit calculation at load powered from the UPS
    By Marijo Ha in forum Electrical & Power Engineering
    Replies: 1
    Last Post: 04-01-2012, 05:50 PM
  5. short circuit duty of power transformer
    By shashank111 in forum Electrical & Power Engineering
    Replies: 0
    Last Post: 10-08-2010, 07:42 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40