    ETAP LV Distribution Boards no Fault Contribution

    Why are there no fault contribution from any of the LV distribution boards even though they have motor loads?


    [link Point to another website Only the registered members can access]


  2. # ADS
    Spons Circuit
    Join Date
    Always
    Posts
    Many
     
  3. #2

    Re: ETAP LV Distribution Boards no Fault Contribution

    check study case options.

  4.    Sponsored Links



    -

  5. #3

    Re: ETAP LV Distribution Boards no Fault Contribution

    The motors are very small in kW size.

    5.5 kW @ 400V = 8 Amps

    Assuming a motor impedance of 20% the injected fault current is approximately 5 per unit.

    Given the full load current of the motor is so low and the high level of fault current being supplied from the incoming supply this will dominate and you are not going to see very much contribution from the motors.

    If you do a test and change the motors to 500 kW you will see 3-5 kA injected at the main bus from each motor.

  •   

Similar Threads

  1. Replies: 0
    Last Post: 12-19-2017, 02:03 AM
  2. How Do I Tackle This Problem - Urgently Contribution Please!
    By petengine in forum Oil And Gas Production
    Replies: 0
    Last Post: 11-17-2016, 01:54 PM
  3. Lifting Lug Contribution
    By lgwsaw in forum Engineering Spreadsheets & Presentations
    Replies: 15
    Last Post: 04-18-2016, 02:04 PM
  4. Earth-fault proteciont 67n with etap 7.5
    By Young.Engineer in forum Electrical & Power Engineering
    Replies: 7
    Last Post: 05-01-2014, 04:39 AM
  5. book and ISA, a small contribution to this forum
    By nhan in forum Safety And Environment
    Replies: 10
    Last Post: 12-10-2008, 10:02 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •