Hello to all!
I'm modelling a big (about 10km of cables) electrical network with ETAP 7.5 and I'm testing the earth-fault directional protections 67N.
There is one MV forniture, and the network is used in ring form.
My problem is this: if I simulate an earth-fault in the supply source (outside my network), ETAP doesn't calculate the CAPACITIVE current that flow between the network and the supply source (contribution of the network to the supply fault).
The neutre is compensated with Petersen coil, so a few amperes current has to flow, and this current could trip the first protection giving a black-out in all my network even though the fault is outside.
Anyone know how to simulate this capacitive current with ETAP??
Thanks!![]()