Thread: what is the calculation procedure for sizing of earthing busbars?

  1. what is the calculation procedure for sizing of earthing busbars?

    There is an standard for sizing earth bars?

    [link Point to another website Only the registered members can access]


  2. # ADS
    Spons Circuit
    Join Date
    Always
    Posts
    Many
     
  3. #2
    Look for adiabatic equation. I use the new cdegs 2012 , one of the modules. Can do it for you , just send me short circuit current and voltage and material used.


    Sent from my iPhone using Tapatalk

  4.    Sponsored Links



    -

  5. Re: what is the calculation procedure for sizing of earthing busbars?

    ???????????

  6. #4

    Re: what is the calculation procedure for sizing of earthing busbars?

    Module is called Ampacity. I just checked. You can even use it in DEMO version, but cannot print report.
    Its based on round conductors, but you can just use the rectangular and match the required area.

    This is a sample report from it (I just keyed in some data, for illustration):

    Minimum Conductor Size:
    62.7609 MCM
    31.7938 sq. mm
    0.1252 in (radius)
    3.1813 mm (radius)


    Input Data:

    Symmetrical RMS Current Magnitude: 12 kA

    Maximum Fault Duration: 0.5 s

    Ambient Temperature: 35 °C

    Maximum Allowable Temperature: 1083.0000 °C (fusing temperature)

    Conductor Type: Copper, annealed soft drawn (100% conductivity)

    Decrement Factor: 1.0618
    X/R: 20
    Frequency 50 (Hz):


    Material Constants of Conductor:

    Name: Copper, annealed soft drawn (100% conductivity)

    Reference Temperature for Material Constants: 20.0000 °C

    Thermal Coefficient of Resistivity at Reference Temperature: 0.00393 1/°C

    Fusing Temperature of Conductor: 1083.0000 72

    Resistivity of Conductor at Reference Temperature: 1.7200 mW×cm

    Thermal Capacity per Unit Volume: 3.4200 J/cm³ · °C

  7. #5

    Re: what is the calculation procedure for sizing of earthing busbars?

    Module is called Ampacity. I just checked. You can even use it in DEMO version, but cannot print report.
    Its based on round conductors, but you can just use the rectangular and match the required area.

    This is a sample report from it (I just keyed in some data, for illustration):

    Minimum Conductor Size:
    62.7609 MCM
    31.7938 sq. mm
    0.1252 in (radius)
    3.1813 mm (radius)


    Input Data:

    Symmetrical RMS Current Magnitude: 12 kA

    Maximum Fault Duration: 0.5 s

    Ambient Temperature: 35 °C

    Maximum Allowable Temperature: 1083.0000 °C (fusing temperature)

    Conductor Type: Copper, annealed soft drawn (100% conductivity)

    Decrement Factor: 1.0618
    X/R: 20
    Frequency 50 (Hz):


    Material Constants of Conductor:

    Name: Copper, annealed soft drawn (100% conductivity)

    Reference Temperature for Material Constants: 20.0000 °C

    Thermal Coefficient of Resistivity at Reference Temperature: 0.00393 1/°C

    Fusing Temperature of Conductor: 1083.0000 72

    Resistivity of Conductor at Reference Temperature: 1.7200 mW×cm

    Thermal Capacity per Unit Volume: 3.4200 J/cm³ · °C

  8.    Spons.


  •   

Similar Threads

  1. UG-39 calculation : Procedure to take care in Pvelite
    By shm8324 in forum Mechanical Engineering
    Replies: 12
    Last Post: 04-29-2018, 10:17 PM
  2. earthing calculation
    By farchan in forum Electrical & Power Engineering
    Replies: 6
    Last Post: 11-15-2013, 04:39 AM
  3. earthing calculation for plant as per IEE
    By saraswatapalit in forum Electrical & Power Engineering
    Replies: 0
    Last Post: 06-09-2013, 09:21 AM