Thank for your response.
please see below picture for my configuration.
[link Point to another website Only the registered members can access]
my calculation :
R=Ï/2Ï€L [log_e [8L/d]-1]
Where
R : the resistance of rod or pipe, in ohms (Ω)
L : the length of the rod or pipe, in meters (m) = 15 m
d : the diameter of the rod or pipe, in meters (m) = 0.0603 m
Ï : the soil resistivity in ohm meters (Ω-m) = 244 ohm-m
Substituting the values.
R=244/(2Ï€×15) [log_e [(8×15)/0.0603]-1]
R=2.5889 [7.5959-1] Ω
R=17.076 Ω
According to BS 7430, Resistance of vertical parallel:
R_n=R[(1+λa)/n] => a=Ï/2Ï€Rs
Where
Rn : the resistance of multiple electrodes
R : the resistance of one electrode in isolation, in ohms (Ω) = 17.076 Ω
s : the distance between rods, in meters (m) = 8.25 m
Ï : is the resistivity of the soil, in ohm meters (Ω-m) = 244 Ω-m
λ : A factor for electrodes
: an hollow square = 7.65 (refer to BS 7430 table 2)
: parallel in a line = 1.66 (refer to BS 7430 table 4)
n : no. of electrodes arrange
The resistance of rod electrodes in hollow square R1:
a=244/(2×Ï€×17.076×8.25)
a=0.252686
R1=17.076[(1+7.65×0.275657)/9]
R1=5.898 ohm
please whether my calculation is correct or not.
actually in BS7430:2011 page 93, give an example for combination between hollow square and line configuration to reduce the resistance. but i'm still not sure since some value of variables are wrong.
any suggestion?
thank you