    I have an orifice plate calculation which stating that the max DP as 125 mBar at max flow rate 500 m3/hr.
    Accordingly i have calibrated the FT with 0 - 125 mBar and 500 m3/hr.I beleive in the DCS also i should set the range as 0 - 500 m3/hr.Surprisingly our engineering contratctor given the DCS range as 0 - 670 m3/hr.Is this right or not???

    Not : My FT Transfer function set as Square root...


    Expecting immediate responses.....

  2. # ADS
    Spons Circuit
    Join Date
    Always
    Posts
    Many
     
  3. Re: Flow Transmitter Ranges

    The DCS scale should be a linear 0-500m3/hr, with the square root extraction done in the transmitter.

  4.    Sponsored Links



    -

  5. #3

    Join Date
    Feb 2011
    Location
    saudi arabia
    Posts
    210

    Re: Flow Transmitter Ranges

    if the flow rate is 0 to 500 m3/hr then the DCS range should be equal, otherwise the process measurement will be the same.

  6. Re: Flow Transmitter Ranges

    this video shows how to calibrate 3051 pressure transmitter :

    [link Point to another website Only the registered members can access]


  7. #5

    Re: Flow Transmitter Ranges

    DCS setting is wrong, must must be 500

  8.    Spons.


  9. #6

    Re: Flow Transmitter Ranges

    Quote Originally Posted by carl_e View Post
    The DCS scale should be a linear 0-500m3/hr, with the square root extraction done in the transmitter.
    square root calculation shall be performed in DCS.

  10. #7

    Re: Flow Transmitter Ranges

    Quote Originally Posted by carl_e View Post
    The DCS scale should be a linear 0-500m3/hr, with the square root extraction done in the transmitter.
    square root calculation shall be performed in DCS.

  11. Re: Flow Transmitter Ranges

    Quote Originally Posted by qdzung View Post
    square root calculation shall be performed in DCS.
    No. That's wrong. The original poster (OP) stated, "My FT Transfer function set as Square root". Go back and read it. So the flow transmitter is doing the square root function.

    Hence, the answer to this thread's question relates to the conditions originally stated.

    Maybe your plant has a policy that square root is done in the DCS. That's fine. Do it that way. But it does not relate to issue of a contractor providing the wrong range value for that point to the DCS.

  12. Re: Flow Transmitter Ranges

    Quote Originally Posted by qdzung View Post
    square root calculation shall be performed in DCS.
    No. That's wrong. The original poster (OP) stated, "My FT Transfer function set as Square root". Go back and read it. So the flow transmitter is doing the square root function.

    Hence, the answer to this thread's question relates to the conditions originally stated.

    Maybe your plant has a policy that square root is done in the DCS. That's fine. Do it that way. But it does not relate to issue of a contractor providing the wrong range value for that point to the DCS.

  13. #10

    Re: Flow Transmitter Ranges

    Dear Carl,
    Thank you very much.
    I wrote my comment because I familiar with other specifications.

    Regarding the question from topic, the DCS engineer had made mistakes while input "System range" for this transmitter. The System range should be sam with Calibration range : 0-500 m3/hr. You should request DCS engineer to check this.

  14. #11

    Re: Flow Transmitter Ranges

    Dear Carl,
    Thank you very much.
    I wrote my comment because I familiar with other specifications.

    Regarding the question from topic, the DCS engineer had made mistakes while input "System range" for this transmitter. The System range should be sam with Calibration range : 0-500 m3/hr. You should request DCS engineer to check this.

  15.    Spons.


  •   

Similar Threads

  1. Article: Flow Transmitter Ranges
    By vikkoo7 in forum Home Articles
    Replies: 0
    Last Post: 03-17-2014, 09:25 PM
  2. Transmitter Diaphragm Material selection for Hydrogen Application
    By prajule in forum Instrumentation & Control
    Replies: 1
    Last Post: 11-28-2013, 01:18 PM
  3. Pressure and temperature transmitter
    By giova70 in forum Instrumentation & Control
    Replies: 6
    Last Post: 04-05-2011, 02:27 AM
  4. DP Level Transmitter Rosemount 1151 Smart
    By Sabeur in forum Instrumentation & Control
    Replies: 0
    Last Post: 03-22-2011, 06:03 PM
  5. Level Transmitter
    By jmarek123 in forum Instrumentation & Control
    Replies: 1
    Last Post: 08-23-2010, 05:13 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •