Results 1 to 6 of 6
Thread: Power cable
    Feb 2011
    saudi arabia
    Power cable
    Hi All,
    3x 1C cable lay above the ground from substation to substation, 1 week after commission it was found the tray is over heating. what is the cause of the tray over heating, this single core was lay apart.
    please advise.
    Cy
    Is likely to be due to eddy currents
    But explain best the phenomena with a drawing, were are indicate the dimensions and distances, cable type (armour, unarmour) voltage, current, path length, etc.
    The cable is in trefoil or laid in flating formation (separate or touching)?
    the formulas to understand the problem can be found in IEC 60287
    bye
    Dec 2009
    Riau, Indonesia
    Wel, overheating means energy, try to look for the energy source, such as :
    1. Electro magnet looping from metal cable ties that forming CT.
    2. single core cable lays in different tray.
    3. ground current from ground "summing" flows through tray to ground
    4. Both ground end of cable is grounded so the cable is heated up
    5. etc.
    But since you mention "single core lay apart", I suppose the magnetic and capacitance is not balance and transfered to tray. Try to implement "INTERPOSING" method.
    Hope this will help you.
    Feb 2011
    saudi arabia
    Hi All,
    This cable is single core connected to main substation to sub substation from 22kv to 6.6kv, distance between 1c cable is 300to400mm.
    Cy
  6. Quote Originally Posted by cytech View Post
    Hi All,
    Cy
    Clear answer. You cannot lay powercables single core segregated.
    Trefoil installation with cleats for dynamic forces is the only solution.
    Red face ^^
    Please check list :
    1. Connection all point.
    2. Current in grounding. <<< The most of problem.
    3. However , if Temperature are not anymore from cable data sheet specification, you 're not serious.
  1. Power and Instrument Cable
    By cytech in forum Electrical & Power Engineering
    Last Post: 03-25-2012, 12:26 PM
  2. Cable szing small power (Instrumentation)
    By instsuresh in forum Instrumentation & Control
    Last Post: 10-15-2011, 01:42 PM
  3. Cathodic cable
    By cytech in forum Materials Science &Corrosion
    Last Post: 05-19-2011, 03:58 PM
  4. cable route
    By Alex_1986 in forum Instrumentation & Control
    Last Post: 12-08-2010, 09:23 AM
  5. Contactor Drop off Problem in Long Distance control Cable. cable capacitance
    By raj151857 in forum Electrical & Power Engineering
    Last Post: 10-29-2010, 05:38 PM