Lately, i am having doubts in simulation of short circuits regarding PV plants.
PV will be connected to inverters and then to a step up transformers then maybe another step up transformers until we can met the kV level at the connection point.
Upon simulation most inverters are modelled as 1.0/Isc as impedance with a voltage source of 1.0pu.. I have tried this in etap, neplan, and others.
But according to a book, by Tleiss, it is said said that inverters are modelled as current source rather than voltage sources. It is said that applying the 1.0/Isc will only be applicable if the fault is on the inverters ac side terminals.
Can anyone give an idea on if it is possible to model current sources on etap or an software aside from digsilent?
Sent from Mars