Thread: Siemens 7RW600 Overflux Protection Setting

  1. Siemens 7RW600 Overflux Protection Setting

    Hi,

    Can someone explain to me how to interpret these settings applied to protect a generator against overfluxing? Below are the settings and calibration test results.

    s01_FREQ= 60 s01_UN= 120 s01_T_TRP= 0.10
    s16_U1_PROT$= "ON" s16_U1= 84 s16_T_U1= 2.00
    s29_UF_PROT$= "ON" s29_UF1= 1.10 s29_T_UF1= 10.00
    s29_UF2= 1.30 s29_T_UF2= 5.00 s29_T_1.10= 350
    s29_T_1.15= 125 s29_T_1.20= 40 s29_T_1.25= 15
    s29_T_1.30= 5 s29_T_1.35= 0 s29_T_1.40= 0
    s29_T_RES= 900 s29_K_ADD= 1.00 s64_CMD_RELAY$= "ON"
    s64_CMD_1_1$= "UF1 TRIP"s64_CMD_1_2$= "UFT TRIP"s64_CMD_2_RELAY$=
    "ON"
    s64_CMD_2_1$= "UX TRIP"s64_CMD_2_2$= "U1 TRIP"

    Relay Test Results for: 27 UNDERVOLTAGE PU (U1)
    PICKUP VOLTS IDEAL %ERROR OK?
    48.497 48.497 0.00 PASS

    Relay Test Results for: 27 UNDERVOLTAGE TIMING (T U1)
    MULTIPLE VALUE TIME(CY) TIME(SEC) IDEAL %ERROR OK?
    0.93 45.103 122.47 2.041 2.000 2.06 PASS

    Relay Test Results for: 24 V/HZ TRIP PU (UF2)
    PICKUP VOLTS IDEAL %ERROR OK?
    157.560 156.000 1.00 PASS

    Relay Test Results for: 24 V/HZ TRIP TIMING (T FU2)
    MULTIPLE VALUE TIME(CY) TIME(SEC) RANGE OK?
    1.20 187.200 319.44 5.324 4.725 TO 5.525 PASS


    I'm just particular with the overfluxing protection. Thanks.

  2. # ADS
    Spons Circuit
    Join Date
    Always
    Posts
    Many
     
  3. #2

    Re: Siemens 7RW600 Overflux Protection Setting

    Much better if we relate it to DIGSI software of Siemens:

    Sample screenshot:

    [link Point to another website Only the registered members can access]

    As for test results, you need to have it in for work scope to include result explanation from the contractor to understand. We don't know how/what. Ask yourself "AM I ONLY OKAY WITH THE PASS OR FAIL RESULT?".


  4.    Sponsored Links



    -

  •   

Similar Threads

  1. Siemens NX 9.0
    By hermes in forum Mechanical Engineering
    Replies: 1
    Last Post: 06-05-2014, 10:10 PM
  2. Siemens Cemat 7
    By knight282011 in forum Instrumentation & Control
    Replies: 0
    Last Post: 07-27-2012, 08:32 PM
  3. Setting HSE KPIs
    By Mohammed Dalta in forum Safety And Environment
    Replies: 1
    Last Post: 06-08-2011, 05:43 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •