    I have problems for the cap bank explosion. We use the cap bank to reduce the power factor not to exceed the required limitation. However, some of capacities were exploded for some reasons. Someone said that because of the harmonic issues. Can anyone give me suggestion to remedy this problems.

    Rgds,
    Nutcha

  2. # ADS
    Spons Circuit
    Join Date
    Always
    Posts
    Many
     
  3. #2
    How are the capacitors connected?


    Sent from my iPad using Tapatalk

  4.    Sponsored Links



    -

  5. #3

    Join Date
    Nov 2010
    Location
    Sweden
    Posts
    768

    Re: Cap Bank

    Quote Originally Posted by nutcha View Post
    Hi All,

    I have problems for the cap bank explosion. We use the cap bank to reduce the power factor not to exceed the required limitation. However, some of capacities were exploded for some reasons. Someone said that because of the harmonic issues. Can anyone give me suggestion to remedy this problems.

    Rgds,
    Nutcha
    you should install a PQ Meter for 1 week in order to find the best solution for your problem.

  6. #4

    Re: Cap Bank

    As raw said - install a PQ meter for a period of time. Have a look at the harmonics/events. You will find your answer quickly.

  7. #5

    Re: Cap Bank

    If your network contains harmonics you can install a harmonic filter. Another solution is to install capacitors with a rated voltage higher than the existing ones. These solutions must be verified by knowing perfectly the quality of energy. Contact the supplier of power factor corrector to find a customized solution

  8.    Spons.


  9. #6

    Join Date
    Nov 2010
    Location
    Sweden
    Posts
    768

    Re: Cap Bank

    AGAIN .......... you should install a PQ Meter for 1 week in order to find the best solution for your problem. Later contact me when you have the data

  10. #7

    Join Date
    Nov 2010
    Location
    Sweden
    Posts
    768

    Re: Cap Bank

    AGAIN .......... you should install a PQ Meter for 1 week in order to find the best solution for your problem. Later contact me when you have the data

  11. Re: Cap Bank

    harmonics

  12. Re: Cap Bank

    Hi,

    How is the capacitor bank connected? Is the capacitor bank at distribution level or in an industrial plant? There might be certain causes for the explosion which includes:
    a. Transient Overvoltage
    b. Capacitor Energization/Switching
    c. Harmonics

    The first item might be experienced when there is a ground fault located within the capacitor bank installation. The second one is when the inrush current is very large that it exceeds the rate of inrush rating of the capacitor bank. The last item is experienced when the capacitor bank is not sized properly i.e. no impedance/frequency scan conducted.

    Let me know your insights here. Thanks.

    Regards,

Similar Threads

  1. Replies: 0
    Last Post: 01-04-2014, 10:42 PM
  2. Replies: 0
    Last Post: 10-08-2013, 07:42 PM
  3. Replies: 0
    Last Post: 04-18-2013, 10:21 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40