  1. Post Signal Cable Sizing for Analyser

    Dear All,

    I am having an installation of Ammonia analyser in a plant where the PLC is located 600 mtrs away form the instrument/ analyzer to be installed. The analyzer is working on 110V AC power supply & having analog signal 4-20 mA output and a Digital output FAULT ALARM.

    Please help to size the signal cable in this scenario.
    Last edited by sijojoy; 11-11-2015 at 05:39 PM. Reason: Wrong Title

  2. # ADS
    Spons Circuit
    Join Date
    Always
    Posts
    Many
     
  3. Nobody to give an advise???


    Sent from my iPhone using Tapatalk

  4.    Sponsored Links



    -

  5. #3

    Re: Signal Cable Sizing for Analyser

    It depends on your cables specification, you should contact your vendor to get the cable parameters.

    For 110 VAC power supply, you should verify the voltage drop.
    I think it's will be ok for analog (4-20mA) and Discrete status. (it's better to verify again)

    I believe all such requirements are available in Project specifications.

  6. Is there any online tool to size cables for dc voltage???


    Sent from my iPhone using Tapatalk

  7. Re: Signal Cable Sizing for Analyser


    Dear Sijojoy,

    - First of all, you need to specify that either the signal cable will be laid under ground or will it be laid overhead using cable trays? An important aspect is the classification of the area where this cable will be laid. Is it a hazardous area or not?

    - For under-ground cables you have to use armored cable. As far as sizing of the cable is concerned, you can use 18-20 AWG (or 1 mm2) cables for both 24 Vdc signals (Analog & Digital).

    - You can also use multicore cable in your case but harmonics of analog signal can affect the DI signal so it is better to use separate cables for these signals or you can also use a special purpose multicore cable that gives isolation b/t its pairs.

    Last edited by s.hassanjawad; 12-26-2015 at 06:21 PM.

  8.    Spons.


  9. Re: Signal Cable Sizing for Analyser


    Dear Sijojoy,

    - First of all, you need to specify that either the signal cable will be laid under ground or will it be laid overhead using cable trays? An important aspect is the classification of the area where this cable will be laid. Is it a hazardous area or not?

    - For under-ground cables you have to use armored cable. As far as sizing of the cable is concerned, you can use 18-20 AWG (or 1 mm2) cables for both 24 Vdc signals (Analog & Digital).

    - You can also use muticore cable in your case but harmonics of analog signal can affect the DI cable so it is better to use separate cables for these sigals or you can also use special purpose multicore cable that gives isolation b/t its pairs.


Similar Threads

  1. Iec 61285 safety of analyser shelter
    By massimo in forum Instrumentation & Control
    Replies: 7
    Last Post: 04-14-2015, 05:06 AM
  2. Eclipse Graf Free Analog
    By temr in forum Reservoir
    Replies: 13
    Last Post: 09-01-2014, 09:25 PM
  3. Analog for Fiedbus instrument
    By blackbass in forum Instrumentation & Control
    Replies: 0
    Last Post: 08-16-2014, 07:44 AM
  4. Gas Chormatograph Analyser for gas pipeline
    By nutcha in forum Instrumentation & Control
    Replies: 1
    Last Post: 03-10-2014, 05:51 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40