I use DIgSILENT PowerFactory to simulate grids. But I have the problem that a YYn0 transformer has a Z0 (zero sequence impedance) of 60.88% and impedance transformer 7.42%. By modeling this phase fault current is less than 100 Amp., To obtain the events of the recloser installed on the network can observe single-phase fault current of 829 Amp., This value you can get from PowerFactory if box write zero sequence impedance 0.6088%. I would like to help me if anyone has had these problems and how resolved, and I read the IEC standards and can not find a solution. Thank you.