    Re: Article: Arrangement of discharge piping from Pressure Relief Valves

    Hi
    Upward slope is not allowed for PSV discharge line. if the outlet is supposed to discharge to a elevated header, you should put the PSV at an elevation higher than the header but be careful about pressure-loss of PSV inlet line. It should be less than 3% of inlet pressure also consider liquid head in PSV inlet.