    Do you have an idea how to install a grounded thermocouple in an intrinsically safe circuits, IEC60079-14 provides some guidelines, but I am not sure what the real requirements are , could they be used in EPL "Ga" when they are connected to Rosemount 3144P temperature transmitter? is Galvanic isolation on the transmitter a must or 500Vrms isolation would be enough?

    Thank you all in advance,

  2. # ADS
    Spons Circuit
    Join Date
    Always
    Posts
    Many
     
  3. Re: Grounded thermouple in intrinsically safe circuits

    My charts tell me EPL GA is zone (gas) 0. Device Category 1G is for Zone 0.

    Rosemount's 3144P Reference Manual 00809-0100-4021, Rev GB states certification ATEX zone 0 certification 1G:
    I1 ATEX Intrinsic Safety (Zone 0)
    Certificate Number: BAS01ATEX1431X
    ATEX Category Marking II 1 G
    Ex ia IIC T6 (Tamb = –60 to 50 °C)
    Ex ia IIC T5 (Tamb = –60 to 75 °C)
    Special Conditions for Safe Use (x):
    The transmitter is not capable of withstanding the 500 V insulation test as defined in Clause 6.3.12 of EN60079-11. This condition must be taken into account during installation.

    Quick Start Guide, 00825-0100-4021, rev. HA, February 2013 has wiring for grounded and ungrounded thermocouples.

    You still need a barrier/isolator for that is suitable for the transmitter's entity parameters.

  4.    Sponsored Links



    -

  5. Re: Grounded thermouple in intrinsically safe circuits

    In IS applications , For fast response application grounded thermocouples (Ex e or d) should be used with a Eex ia transmitter and IS isolator at the system side.

Similar Threads

  1. Intrinsically Safe Equipment in Ex environment
    By intergrasa in forum Safety And Environment
    Replies: 0
    Last Post: 05-24-2011, 05:49 PM
  2. digital camera intrinsically safe
    By trifilo in forum Oil And Gas Production
    Replies: 2
    Last Post: 07-20-2009, 12:31 AM
  3. digital camera intrinsically safe
    By trifilo in forum Safety And Environment
    Replies: 2
    Last Post: 07-20-2009, 12:31 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40