We have a 5.5kV network in our offshore plateform. I do all electrical simulation with ETAP 7.5 Software. I have some questions:
- We have 4 generators in service with relay protection. And in each generator incomer we have another relay. In case of fault between generator and 5.5kV busbar I opte to use ANSI 67 function to isolate faulted incomer. ANSI 50 can be desactivated or no. Also for setting, I chose In and the time delay (0.15s) that allow it to trip before the ANSI 50 of other incomers trip (2s)..
- In ETAP software, to allow the two function 50 and 67 I must use two separate relays!!
- Setting of 59N and 67N for isolated neutral system.
NB: we have 2 generators of 5MW and 2 generators of 2.5MW.
Thanks for your help