  1. Question: E-Motor Ex Proof Selection

    Salam to all,

    Is there anybody who could explain how selection of ex proof for motor is done?

    There are Ex 'e, Ex 'n, Ex 'p, etc...

    But how exactly we choose any of those to fit the area (Zone 1, Zone 2, etc.)

    General explanation on this matter shall be appreciated.

    Thank you in advance.

  2. # ADS
    Spons Circuit
    Join Date
    Always
    Posts
    Many
     
  3. #2

    Join Date
    Jun 2008
    Location
    Karachi, Pakistan
    Posts
    132

    Re: Question: E-Motor Ex Proof Selection

    Dear Kurt.rock,
    In Industry a large range of liquids, vapours and gases that form explosive mixtures when combined with air, pose a great explosion hazard if a source of ignition through spark, heat or similar energy is present.
    Wherever such gases are processed, stored, transported, dispensed or vented such explosion hazard is present. In case the mixture of explosive gas to air is within the range of explosion, that atmosphere is called "Classified Area," and is a 3D envelope surrounding the source of explosive gas. Explosion Protection is the science and engineering of preventing such explosions. Ex 'e", Ex 'd' etc are all mitigation measures for avoiding these explosion risks.

    Your question is not just limited to electric motors but all electrical and instrumentation equipment (E&I or I&E) installed in explosion classified areas.
    Selection of I&E equipment in classified environment is really not that difficult, if the installation is properly classified. However, the Design/Maintenance Engineer must have sufficient knowledge about the risks, safety measures, which engineering standards are applicable, what is area classification, which mitigation measures are permitted, what maintenance must be done to ensure integrity of the mitigation measures, etc

    International Electrotechnical Commission's (IEC) 60079 series of Standards are one of the most widely applied for all aspects of risks due to explosive gases. The most important being:
    IEC 60079- Electrical Apparatus for Explosive Gas Atmospheres
    • Part 0 General requirements
    • Part 1 Construction and test of flameproof enclosures of electrical apparatus
    • Part 2 Electrical apparatus - type of protection ‘p’
    • Part 3 Spark test apparatus for intrinsically safe circuits
    • Part 7 Increased safety ‘e'
    • Part 10 Classification of hazardous areas
    • Part 11 Construction and test of intrinsically safe and associated apparatus
    • Part 14 Installation (and selection) of equipment in hazardous areas
    • Part 17 Inspection and maintenance of equipment

    You will be able to find these Standards, books etc on this very forum, if you use the key words used in my reply.

    Sajid Ali Khan

  4.    Sponsored Links



    -

  5. Re: Question: E-Motor Ex Proof Selection

    Dear Sajid Ali Khan

    Thank you very much for your comprehensive explanation. Your response as in above shall definitely be informative.

    Regards,

Similar Threads

  1. Motor selection for pumps
    By sebaversa in forum Pipeline And Fluid Flow
    Replies: 0
    Last Post: 05-07-2014, 09:30 PM
  2. Flame proof Vs Explosion Proof
    By SA_FETY in forum Safety And Environment
    Replies: 9
    Last Post: 10-03-2012, 07:27 PM
  3. CSWIP New Question Pattern and Model Question Paper needed.
    By vijay1583 in forum Mechanical Engineering
    Replies: 4
    Last Post: 07-26-2012, 10:35 PM
  4. My payment proof from RewardingWays.com
    By djhurtis in forum Computer & Internet
    Replies: 1
    Last Post: 02-20-2012, 07:35 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40