[IMG]http://www.********.ca/ce5_fh/5-1.jpg[/IMG]INTRODUCTION. The purpose of a fired heater is very simple: To add heat to a process fluid. Its representation on a process flow diagram is also very simple. But, of course, fired heaters are among the most complex pieces of process control equipment. Each furnace is, after all, at least two pieces of equipment in one. Firstly, it is a special variant of the shell and tube heat exchanger since its purpose is to exchange heat. Secondly, it is a chemical reactor in which fuel and air undergo extremely exothermic reactions to produce the required heat.
In previous articles of this series1, 2, 3, 4, the process aspects of controlling a piece of equipment were presented before dealing with protection and safety. This time the topics will be reversed: In the case of fired heaters, it must be safety first!
SAFETY. If fired heaters had not been invented and were being proposed for the first time, I would probably say, "You've got to be kidding. That thing will blow up in your face the first time you throw a match in it." However, at least a half a billion gas fired heaters are in service around the world (according to the American Gas Association). Most of them are operated by people with no technical experience whatsoever; few heaters blow up. Still, the average domestic water heater is not in the same league as a hydrogen reformer furnace. The fact that accidents and disasters are as few as they are, is due to the long experience the human race has in dealing with fire. A million years, I'm told. For the last century, this experience has been embodied in various codes and standards that have been written into law and are en-forced by inspectors around the world.
THE CODE. The most popular, or notorious, of these codes in North America is NFPA 855 and 866 issued by the National Fire Protection Association. These have been considerably updated in recent years, especially in terms of clarity. Nevertheless, there is still the problem of interpretation. The code is not at all easy to read as it combines many facets of construction, instrumentation and operation in a single document. Not only that, but the code5 contains the following disclaimers:
It is not possible for these standards to encompass specific hardware applications, nor should these be considered a "cookbook" for the design of safety systems.
and:
This standard applies to boilers with a fuel input of 12,500,000 Btu/hr (3663 kW) or greater. This standard applies only to boiler-furnaces using single burners firing:
a) Natural gas only as defined in Chapter 3.
b) Other gas with a BTU value and characteristics similar to natural gas.
c) Fuel oil of No. 2....
and:
Furnaces such as those of process heaters used in chemical and petroleum manufacture, wherein steam generation is incidental to the operation of a processing system, are not covered in this standard.
What is an engineer to use for a guide when the furnace is not a boiler, but a feed heater; does not exceed 12½ million Btu/hr, but is only four million; does not burn natural gas as defined in Chapter 3; but refinery off-gas with a high hydrogen content? Despite the disclaimers, the NFPA series is still an excellent guide to the instrumentation and control of any furnace.
FUEL GAS FIRED, SINGLE BURNER FURNACES. The NFPA standard deals with a variety of fuels, both oil and gas. The discussion that follows restricts itself to fuel gas fired, single burners. NFPA standards have been followed as much as possible and have sometimes been exceeded by adding components and control functions where the special requirements of process control make it advisable.
Figure 5-2, shows the in-line instruments typically installed on a burner fuel gas train. Diamond symbols with an "I" in them refer to I/O of the Burner Management System (BMS).
[IMG]http://www.********.ca/ce5_fh/5-2.jpg[/IMG]
FUEL GAS SUPPLY INSTRUMENTS
PCV-1 The fuel gas supply regulator is only required when the fuel gas pressure must be reduced in two stages. This is often the case in refinery service. See Figure 5-3 for typical regulator settings.
PI-1 Every regulator should have a gauge so that the operator
can set the regulator properly and so that he can know that it is doing its job.
PSV-1 Many standard fuel gas train components have an upper pressure limit of approximately 100 psig (700 kPag). Failure of both PCV-1 and PCV-21 would overpressure the fuel gas train if the supply pressure exceeds the rating of any downstream component. In such cases provision for pressure relief is required. Note that it is not unusual to consider double jeopardy in burner safety analysis.
FE-3 This is the place to put fuel gas metering, if required. NFPA puts the fuel gas meter on the main gas line down-stream of the main gas regulator. But when using accurate fuel/air ratio control it makes sense to include the pilot as part of the total fuel supply as it may supply as much as 10% of the total fuel.
PT-3 Large burners with a variable fuel gas supply pressure may require pressure, and possibly even temperature, compensation for the fuel gas measurement.
[IMG]http://www.********.ca/ce5_fh/5-3.jpg[/IMG]
PILOT GAS LINE INSTRUMENTS
PCV-11 The pilot gas regulator is set for the actual required pilot gas pressure.
PI-11 Of course the regulator has a gauge!
BV-14 On small burners, the first pilot shutoff valve may be a standard industrial, two port, solenoid valve. Limit switches can be considered optional on solenoid valves.
On large burners, a burner safety shutoff valve is generally the preferred choice. These valves have an internal spring to force the valve shut, a solenoid to hold them open, and a small motor to re-open the valve. Item BV-24, following, provides more detail concerning this type of valve.
Some installations use a standard, industrial, diaphragm operated control valve. In either case, the valve must be fail-closed.
ZSC/O-14 At least one limit switch is required on BV-14 if it is anything more than a simple solenoid valve. This is needed to prove that the valve is shut during the purge phase. For failsafe operation it is best to have a limit switch at each end of travel. The upper limit switch proves that the valve is fully open at all times when the pilot flame is supposed to be on. The article, "Limit Switches Key to Valve Reliability"8 , explains exactly how to connect double, failsafe, limit switches.
BV-15 The pilot vent valve makes certain that there is never any gas pressure on the second shutoff valve despite any leakage through the first one. Since its only purpose is to vent leakage, the vent line has a smaller bore than the supply line. It must be fail-open. The Canadian Gas Association code CAN/CGA-3.9-M879 repeats the following table from NFPA 86A 7 for determining vent line sizes:
| |
|
| |
|
|
|
| |
|
|
|
| |
|
|
|
| |
|
|
|
| |
|
|
|
| |
|
|
|
| |
|
|
|
| |
|
|
|
| |
|
|
|
| |
|
|
|
| |
|
>15 % line cross-sectional area |
For low molecular weight fuels such as hydrogen (Mol. Wt. = 2) or methane (Mol. Wt. = 16) it is sufficient to vent the valve to atmosphere outside the building. For fuels heavier than air, such as ethane, propane and butane (Mol. Wt. = 30, 44, 58 respectively), the vent should be piped to a flare header.
Using the table above, it may be determined that a ¾" or 1", simple solenoid valve is sufficient. If not, a fail-open burner safety valve should be used. It operates in a similar, but opposite, manner to BV-14.
ZSC/O-15 Limit switches should be included and incorporated in the BMS logic, if a full-sized vent valve is required.
BV-16 The second pilot shutoff valve is identical to the first, BV-14.
ZSC/O-16 Limit switches should be included and incorporated in the BMS logic, if a full-sized, second pilot valve is required.
PI-18 The final pressure gauge confirms that all valves are in their correct position and that the appropriate pressure is available for the pilot flame.
BY-18 The igniter itself is essentially a spark plug powered by a high voltage transformer. It is capable of sparking continuously as required by the BMS.
BSLL-19 The pilot flame detector is used to confirm that the pilot light has ignited and is burning in a stable manner. A variety of types exist depending on the size of the burner and the type of fuel.
A flame rod is a simple electrode that projects into the flame. An electric current passes through the flame to the pilot gas nozzle and energizes a sensitive relay or electronic circuit. Since it only senses flame at a point, it will not detect the main flame. A disadvantage is that the tips burn off after a period of time and a nuisance trip of the furnace will result.
An ultra-violet (UV) flame detector is probably the most popular on process heaters. It is, however, a rather complex device that requires certain precautions for reliable operation. UV detectors are optical devices. A lens in front must be aimed directly at the flame. Depending on the particular arrangement used, it may or may not be desirable for the detector to "see" only the pilot flame or the main flame as well. One or more viewing windows, BG-45A to X, must be provided by the furnace fabricator to assist in aligning the detector. UV detectors are mounted on ball swivels to permit accurate alignment. An instrument air purge complete with a rotameter and a needle valve should be connected to the tube between the lens and the flame in order to prevent dust from accumulating on the lens and to cool it. Some units also require a supply of cooling water.
FUEL GAS LINE INSTRUMENTS
PCV-21 The main gas regulator is set to the maximum allowable fuel gas pressure for the main burner.
PI-21 Every regulator requires a pressure gauge. This gauge is also used to adjust the setpoints of PSLL-22 and PSHH-27.
PSLL-22 The fuel gas low pressure switch prevents the operator from attempting ignition when there is insufficient pressure to complete it. The upstream location is so that it is not necessary to bypass its function during the ignition sequence.
BV-24 The first fuel gas safety shutoff valve is one of the "safety shutoff valves". It must be especially certified for fired heater use. The first of the three valves in the main gas train has a manual reset and a solenoid that function as follows:
- When the solenoid is de-energized the valve is shut and the manual reset has no function whatsoever.
- When the solenoid is energized, the valve remains shut until the manual reset is lifted.
- Lifting the manual reset opens the valve. The valve then remains open as long as the solenoid is energized.
A valve with this function is sometimes termed a "free handle" valve. Once a trip has occurred, the manual reset on the first safety shutoff valve will prevent the burner from reigniting. This is an extremely important safety feature. Even if there is insufficient pressure to maintain a flame, unburned gas may still collect in the firebox and ignite with explosive force once a large quantity has accumulated
ZSC/O-24 In addition, BV-24 requires a limit switch to prove that it is shut during the purge and ignition phases. Item ZSC/O-14, above, details the requirements of fail-safe limit switch arrangements.
BV-25 The fuel gas vent valve has similar criteria to those of BV-15. The same sizing table applies.
ZSC/O-25 These limit switches are optional, depending on the size of the vent valve.
BV-26 The second main gas safety shutoff valve is a little different from the first in that it does not require a manual reset. The automatic reset feature is accomplished by a small electric motor that opens the valve as soon as it is energized. The valve fails closed upon de-energization. Automatic reset valves are identified by the little "M" instead of the "S" in the symbols on Figure 5-2. The valve may incorporate a slow opening feature. Power to the reset motor should be disconnected as soon as the valve is open so that a momentary power loss to the solenoid does not cause the valve to cycle.
ZSC/O-26 BV-26 should also have limit switches whose status is incorporated into the BMS logic.
PSHH-27 The fuel gas high pressure switch shuts down the main furnace when the fuel gas pressure exceeds the maximum allowable for a stable flame. Excessively high pressure can blow the flame out only to have it reignite, perhaps explosively, higher up in the furnace.
There is a trend toward the use of analog transmitters instead of switches for sensing process values, even for shutdown purposes. The trip value is then programmed into the control system instead of being adjusted at the switch. Transmitters have become more reliable than switches and also provide much more information10 . If this is the policy at your installation, the functions of PSLL-22 and PSHH-27 can be combined in a single transmitter located at PSLL-22. A second transmitter can then be used to provide pre-alarms or an automatic redundancy scheme.
FV-3 Most large industrial furnaces have a gas flow control valve to modulate the heat input. Details of the control system are discussed in the sections on fuel control. The gas flow control valve must be fail-closed but must also have some means of ensuring that it does not shut too closely to the seat or an unstable flame will result. Approximately 35% of full flow is a typical minimum. Some engineers program a minimum output into the control system. Others weld a small stop onto the shaft. Software blocks can be easily altered and welded stops may not be re-installed when the valve is replaced. I use both. The software limit has the advantage that it can be raised if the original setting is too low. It should be set slightly higher than the welded stop in order to inhibit reset windup before the 0% controller output is reached.
Furnaces with cyclical service, such as those used in dryer regeneration service, may have the main flame turned on and off on a regular basis. In such cases, there cannot be a minimum stop on the control valve. Instead, logic should be provided that shuts the valve fully whenever the controller tries to position it below the minimum flame setting. The controller must also be switched to manual to prevent reset windup whenever this is done.
ZSC-3 The gas flow control valve requires a limit switch to confirm that it is at the minimum flow position before lightoff. The switch should be set slightly above the minimum stop.
PI-28 A pressure gauge should be placed last before the fuel nozzle itself to provide assistance in diagnosing mysterious problems. Dirt does collect in valves and other places!
BSLL-29 The main flame detector is generally of the combination ultra-violet and infra-red (UV/IR) type. The same requirements apply as to the UV detector for the pilot.
Burners in cyclical service do not require a main flame detector. They rely entirely on the pilot flame detector, which may be adjusted so that it can see both flames.
AIR SUPPLY INSTRUMENTS. There is considerable variation in the air supply system among furnaces of different sizes. Small heaters, and some not so small, may be entirely natural draft and are controlled only with a manually set air damper. For furnaces with forced draft (FD) fans some, or all, of the following instruments are required.
PDSH-31 If the air intake has a filter, it must be fitted with a differential pressure switch or transmitter connected to an alarm to warn of plugging.
FE-32 If the FD fan is large, a flow measurement device is needed at the intake to measure flow through the fan so that surge can be prevented. A simple averaging pitot tube (Annubar) or a thermal device provides sufficient accuracy without significant loss of head.
FV-32 Large fans require a minimum flow blow-off valve to prevent surge.
FE-33 The actual air flow to the burner must be measured if an accurate fuel/air ratio is to be maintained. This is generally done for large furnaces. Smaller packaged units have the fuel and the air linked with cams and no air measurement is done. A previous article1, explains why it is not possible to use same flow element for both minimum flow and throughput flow control. It may be required to use a venturi to achieve both high accuracy and low head loss. On very large burners, arrays of pitot tubes or thermal flow meters distributed across the duct, are the preferred method. However, these can be somewhat time-consuming to install and maintain.
The associated transmitter is also used to provide the pre-alarm for FSLL-36.
FV-33 A fail-open combustion air control valve is placed at the inlet to the wind box for those burners requiring external air control. A butterfly valve is a popular choice. Very large fans may have provision for inlet guide vanes which provide a more efficient means of doing the same thing. The valve requires a minimum stop to prevent complete closure.
ZSO-33 FV-33 has a limit switch to confirm that it is fully open during purging.
VSHH-34 Large fans should be provided with a seismic type vibration switch. A previous article3 discusses these devices. The switch should be connected to shut down the entire system as the heater cannot be operated without the fan. Very large fans may even include an entire bearing vibration monitoring package.
YS-34 The FD fan motor status contact is used to provide information to the BMS.
FSH-35 The purge air switch is used to indicate adequate purge flow. It is usually a differential pressure switch across the wind box, if any, of the furnace or it may be a signal from the flow transmitter, FT-33. As can be seen in Table 5-1, there is a variety of opinions concerning minimum purge requirements.
| Specification |
|
|
|
| ASME Section VII11 |
> 5 minutes |
> 5 volumes |
> 25% full flow |
| API(RP 550 – Part 4)12 |
> 5 minutes |
> 5 volumes |
> 25% full flow |
| NFPA 85015 |
not specified |
> 8 volumes |
> 70% full flow |
| CGA B149.39 |
not specified |
> 4 volumes |
> 60% full flow |
Table 5-1 Minimum Purge Requirements
FSLL-36 The combustion air low flow shutdown switch shuts down the burner if there is insufficient flow for safe combustion.
FURNACE INSTRUMENTS
TE-41 One or more skin thermocouples should be provided on the tubes of the furnace. The thermocouple element is welded directly to the tubes. Note that the device that receives the T/C signal must be capable of accepting grounded signals.
TSHH-42 High stack gas temperature is cause for shutdown. The furnace should also be isolated from the process feed if the feed is flammable. Tube rupture may be the cause for the high stack temperature.
AE-43 For a burner to operate at peak efficiency, stack oxygen and combustibles must be measured and controlled. However, the additional cost and maintenance of stack analyzers limit their use to large burners. High and low alarms should be programmed.
PI-44 A draft gauge must be provided to give a grade level indication of the pressure in the furnace. This is a special type of pressure gauge sensitive to inches of water pressure.
BG-45 A to X
FG-45 A to X Viewing windows were mentioned previously with respect to aligning the flame detectors. Other windows may be needed as well. These are usually made of glass and require a small air purge to keep them cool and clean. Regulators are often used control the air flow. This is rather pointless since it is flow control that is required. The presence of pressure may only mean that the line is plugged. The absence of pressure may mean that the purge is flowing freely at a rate beyond the capacity of the regulator. Pressure alone proves nothing. The appropriate instrument is a rotameter with a needle valve. 15 SCFH is a common flow setting. The rotameter provides proof that purge is actually occurring.
A number of purge rotameters can be mounted on a plate and pre-tubed to a small instrument air header. This greatly reduces field labour and provides a convenient way of checking all purge rates from a single location.