Thread: Steam Heating Processes - Load Calculating
    In general steam heating is used to
    • change a product or fluid temperature
    • maintain a product or fluid temperature
    [h=Changing the Product Temperature - Heating up with Steam]3[/h] The amount of heat required to raise the temperature of a substance can be expressed as:
    Q = m cp dT (1)
    where
    Q = quantity of energy or heat (kJ)
    m = mass of the substance (kg)
    cp = specific heat capacity of the substance (kJ/kg oC ) - Material Properties and Heat Capacities for several materials
    dT = temperature rise of the substance (oC)
    Preferring Imperial Units - Use the Units Converter!
    This equation can be used to determine a total amount of heat energy for the whole process, but it does not take into account the rate of heat transfer which is:
    • amount of heat energy per unit time
    In non-flow type applications a fixed mass or a single batch of product is heated. In flow type applications the product or fluid is heated when it constantly flows over a heat transfer surface.
    [h=Non-flow or Batch Heating]3[/h] In non-flow type applications the process fluid is kept as a single batch within a tank or vessel. A steam coil or a steam jacket heats the fluid from a low to a high temperature.
    The mean rate of heat transfer for such applications can be expressed as:
    q = m cp dT / t (2)
    where
    q = mean heat transfer rate (kW (kJ/s))
    m = mass of the product (kg)
    cp = specific heat capacity of the product (kJ/kg.oC) - Material Properties and Heat Capacities for several materials
    dT = Change in temperature of the fluid (oC)
    t = total time over which the heating process occurs (seconds)
    [h=Flow or Continuous Heating Processes]3[/h] In heat exchangers the product or fluid flow is continuously heated.
    The mean heat transfer can be expressed as
    q = cp dT m / t (3)
    where
    m / t = mass flow rate of the product (kg/s)
    dT = change in temperature of the fluid (oC)
    [h=Calculating the Amount of Steam]3[/h] If we know the heat transfer rate - the amount of steam can be calculated:
    ms = q / he (4)
    where
    ms = mass of steam (kg/s)
    q = calculated heat transfer (kW)
    he = evaporation energy of the steam (kJ/kg)
    The evaporation energy at different steam pressures can be found in the SteamTable with SI Units or in the Steam Table with Imperial Units.
    [h=Example - Batch Heating by Steam]3[/h] A quantity of water is heated with steam of 5 bar (6 bar abs) from a temperature of 35 oC to 100 oC over a period of 20 minutes (1200 seconds). The mass of water is 50 kg and the specific heat capacity of water is 4.19 kJ/kg.oC.
    Heat transfer rate:
    q = (50 kg) (4.19 kJ/kg oC) (100 oC - 35 oC) / (1200 s)
    = 11.35 kW
    Amount of steam:
    ms = (11.35 kW) / (2085 kJ/kg)
    = 0.0055 kg/s
    = 19.6 kg/h
    [h=Example - Continuously Heating by Steam]3[/h] Water flowing at a constant rate of 3 l/s is heated from 10 oC to 60 oC with steam at 8 bar (9 bar abs).
    The heat flow rate can be expressed as:
    q = (4.19 kJ/kg.oC) (60 oC - 10 oC) (3 l/s) (1 kg/l)
    = 628.5 kW
    The steam flow rate can be expressed as:
    ms = (628.5 kW) / (2030 kJ/kg)
    = 0.31 kg/s
    = 1115 kg/h
  3. Thank you!!
  1. Replies: 9
    Last Post: 07-10-2019, 01:40 PM
  2. Replies: 0
    Last Post: 04-10-2014, 10:27 PM
  3. Classification of Steam Heating Systems
    By Esam in forum Pipeline And Fluid Flow
    Last Post: 07-26-2011, 04:55 PM
  4. An introduction to the basic design of steam heating systems
    Last Post: 07-26-2011, 04:54 PM
  5. Calculating Fire Load - Sprinkler Response Time
    By uzbarry in forum Safety And Environment
    Last Post: 02-11-2011, 08:41 AM