Multiple Protection
Many items of EEx rated equipment will employ more than one method of protection in different components of the apparatus. These would be then labeled with each of the individual methods. For example a socket outlet labeled EEx'de' might have a case made to EEx 'e' and switches that are made to EEx 'd'.
Hazardous Locations Classifications Descriptions - ANSI/NFPA(NEC)terms
Class I, Div. 1 - Where ignitable concentrations of flammable gases, vapors or liquids are present within the atmosphere under normal operation conditions.
Class I, Div. 2 - Where ignitable concentrations of flammable gases, vapors, or liquids are present within the atmosphere under abnormal operating conditions.
Class II, Div. 1 - Where ignitable concentrations of combustible dusts are present within the atmosphere under normal operation conditions.
Class II, Div. 2 - Where ignitable concentrations of combustible dust are present within the atmosphere under abnormal operating conditions.
Class III, Div. 1 - Where easily ignitable fibers or materials producing combustible flyings are present within the atmosphere under normal operation conditions.
Class III, Div. 2 - Where easily ignitable fibers or materials producing combustible flyings are present within the atmosphere under abnormal operating conditions.
Common Materials within Associated Class & Group Ratings, such as "Class I, Division 1, Group A":
Class I Areas: Group A: Acetylene / Group B: Hydrogen / Group C: Propane and Ethylene / Group D: Benzene, Butane, Methane & Propane
Class II Areas: Group E: Metal Dust / Group F: Carbon & Charcoal / Group G: Flour, Starch, Wood & Plastic
Class III Areas: NO GROUP: Cotton & Sawdust
For more information see Article 500 of NFPA 70 - The National Electric Code, as published by the National Fire Protection Association.
Equipment category
The equipment category indicates the level of protection offered by the equipment.
Category 1 equipment may be used in zone 0, zone 1 or zone 2 areas.
Category 2 equipment may be used in zone 1 or zone 2 areas.
Category 3 equipment may only be used in zone 2 areas.
Labeling
All equipment certified for use in hazardous areas must be labelled to show the type and level of protection applied.
1. In Europe the label must show: -
a) The CE mark.
b) The code number of the certifying body for the ‘quality certificate’.
c) CE marking is complemented with the Ex mark, followed by the indication of the Group, Category and, if group II equipment, the indication relating to gases (G) or dust (D). For example: - Ex II 1 G (Explosion protected, Group 2, Category 1, Gas)
2. In addition, the normative marking will be able to establish the specific type or types of protection being used, for example: -
EEx ia IIC T4. (Type ia, Group 2C gases, Temperature category 4).
EEx nA II T3 X (Type n, non-sparking, Group 2 gases, Temperature category 3, special conditions apply).
3. The suitability of equipment for the specific hazardous area in the ANSI/NFPA(NEC) regulated market is required to be tested by a NRTL(Nationally Recognized Testing Laboratory). Such institutes are UL, FM or ETL, just to name a few.
a) Dependent on the specific equipment and the applicable division the label will always list the Class(es), Division(s) and may list the Group(s) and temperature Code.
b) Directly adjacent on the label one will find the mark of the listing agency.
c) Some manufacturers claim "suitability" or "built-to" hazardous areas in their technical literature, but in effect lack the testing agency's certification and thus unacceptable for the AHJ (Authority Having Jurisdiction) to permit operation of the electrical installation/system.
4. Also included in the marking are: -
a) The manufacturers name or trademark and address.
b) The apparatus type, name and serial number.
c) Year of manufacture.
d) Any special conditions of use.
e) The NEMA enclosure rating or IP code may also be indicated, but it is usually independent of the Classified Area suitability.
5. Manufacturers will provide specific installation instructions that must be followed for:
a) the equipment to function properly, and
b) to provide the designed protection in the Classified Area according to the listing.
British standards
Industrial electrical equipment for hazardous area has to conform to standard BS 60079 and in some cases, certified as meeting that standard. Independent test houses (known as Notified Bodies)are established in most European countries, and a certificate from any of these will be accepted across the EU. The DTI appoint and maintain a list of Notified Bodies within the UK ([link Point to another website Only the registered members can access]