Results 1 to 7 of 7

Thread: What kind of protection shoul I use in zone 1?

  1. What kind of protection shoul I use in zone 1?

    hello,

    What kind of proteccion should I use in an hazardous zone 1? I must use intrinsically safe circuit, with zener barriers and galvanis protection?

    Thanks

    JP

  2. # ADS
    Spons Circuit
    Join Date
    Always
    Posts
    Many
     
  3. If you use Intrinsic Safety Ex for Zone 1, please use equipment be certified with:
    Ia: Zone 0, 1, 2 allow 2 faults
    Ib: Zone 1, 2 allow 1 faults


    If you use Zener Barrier, please obey this principle:
    Dedicated high-integrity earth: Required
    Safety and Hazardous circuits area: connected
    Field apparatus: 500V IR Test to Earth

    If you use Galvanic Barrier, please obey this principle:
    Safety and Hazardous circuits area: do not connect

  4.    Sponsored Links



    -

  5. Clarify me just a thing,

    But if I have an zone 1, and use "ia"equipment ia (ex. pressure transmiter 4-20mA). I need to have a protection in my control panel that is placed in a non Hazardous area (ex. zener barrier or galvanic isolation"??

    Thanks

    JP

  6. With your pressure transmiter ia 4-20mA in hazardous area, you use Zener barrier in non hazardous area.
    But you also use zener barrier in hazardous area if you put zener barrier in Pressurized enclosure or Flameproof Enclosure.
    Remember Zener barrier and Galvanic barrier are classified as ASSOCIATED APPARATUS.

  7. More one thing, I have to use this protections in nonhazardous area? My question is: If I have the transmitter (Ex) in hazardous area (zone1), the signal come from the transmitter (4-20mA) can enter directly in my control panel without zener barrier or galvanic protections??

    THanks for your help

    JP

  8.    Spons.


  9. Quote Originally Posted by joaopedro View Post
    .....My question is: If I have the transmitter (Ex) in hazardous area (zone1), the signal come from the transmitter (4-20mA) can enter directly in my control panel without zener barrier or galvanic protections??......
    You must connect your transmitter to a zener barrier or isolator located in control room. type [ex Ia] or [ex ib]. This is a requirement to prevent high voltages transferring to the transmitter in the hazardous area in the event of a fault in the controller or high currents in the event of a short circuit or ground fault at the transmitter.

    I personally would chose galvanic isolation over a zener barrier as grounding is not so strict…
    Do not connect signal ground at the transmitter.

    Cheers,
    Iain.

  10. How do you send 4-20mA with Galvanic Barrier to Controller?

Similar Threads

  1. Replies: 1
    Last Post: 10-02-2013, 08:49 AM
  2. Some kind of wonder
    By selmagis in forum Safety And Environment
    Replies: 0
    Last Post: 12-13-2011, 05:00 AM
  3. Check Out For Malware Protection & Spyware Protection
    By asdqw123 in forum Self Improvement
    Replies: 0
    Last Post: 10-15-2011, 09:24 AM
  4. Article: What kind of protection shoul I use in zone 1?
    By joaopedro in forum Home Articles
    Replies: 0
    Last Post: 04-29-2011, 09:55 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40