    Minimum safety distances

    Hello all;

    I case of design of Petroleum storage sites (above ground storage tanks), can anyone guide me to the minimu safety distance requirements for buildings and other related facilities from the tanks?

    I'd also very much appreciate if you'd let me know which is the applicable code/ standard for this.

    many thanks,

  2. # ADS
    Spons Circuit
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many
     
  3. #2
    Locate any tankage containing hydrocarbon or other combustible fluids or gasses a minimum distance of 250'-0" (115m) from any process unit, rail loading facility or truck loading facility.

  4.    Sponsored Links



    -

  5. #3

    Join Date
    Jan 2009
    Location
    Oslo, Norway
    Posts
    83
    Thanks for your response. However, what I am looking for is the minimum distance from a Petroleum tank and an Office building. Can you also let me know the code reference to what you have stated above.

    Regards,

  6. Sandy

    It is best to go for consequence analysis of the said tank and calculate the affected area for the worst case scenario. and then locate the office outside that area

  7. #5
    First determine the consequence analysis results using DNV-PHAST or SHELL-FRED or ALOHA... find the distance of the impact,,,,, then proceed...

  8.    Spons.


  9. #6
    GASCO experience as well as U. S. OSHA Part 1910 and the NFPA (National Fire Protection Association) Code No. 30, but see your local rules as well!

  10. #7

    Join Date
    Jan 2009
    Location
    Oslo, Norway
    Posts
    83
    Thanks for the responses. But you see the tank and the building is already there, what I am trying to comment is if it is safe for the building to be permanently manned? ANother question that comes to my mind is the access to the fire-fighting equipment in case of fire.

  11. #8
    OK - do what Dawood suggested or send me the plot plan of facility.

  12. If the facility is already there still u need to follow same procedure, go for consequence analysis and determine blast overpressures, probable dostances covered by missile fragments and thermal radii. Then ensure that building is constructed against the temp and pressure it may be exposed to.

  13. See NFPA 30, For buidings refer industrial risk insurance guidline.

  14. #11
    look for this doc on

    [link Point to another website Only the registered members can access]


  15.    Spons.


  16. Also - see API RP 752 Management of Hazards Associated with Location of Process Plant, and API RP 753 Management of Hazards Associated with Location of Process Plant Portable Buildings

  •   

Similar Threads

  1. Replies: 18
    Last Post: 01-28-2016, 12:27 PM
  2. safety distances in petroleum facilities
    By srinivas sathya in forum Mechanical Engineering
    Replies: 1
    Last Post: 02-04-2014, 06:15 PM
  3. Fuel Facility distances drom active runways.
    By Zbigmiller in forum Planning & Project Management
    Replies: 0
    Last Post: 08-30-2013, 12:02 AM
  4. Cost-Benefit Analysis of Separation Distances
    By f81aa in forum Safety And Environment
    Replies: 5
    Last Post: 10-22-2012, 11:55 PM
  5. Safety Distances
    By hbili in forum Safety And Environment
    Replies: 7
    Last Post: 02-11-2011, 10:00 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •