Hi taoxianwen123:
The Guidelines for Fire Protection in Chemical, Petrochemical, and Hydrocarbon Processing Facilities by the Center for Chemical Process Safety (American Institute of Chemical Engineers) states in section 7.4.1.2. Tanks and Reservoirs "Automatic refilling using an automatic float valve should be provided. A maximum refill time of 8-hours is recommended (NFPA 22)". Although this book mentions that NFPA 22 recommends 8 hours, the latter considers this time as mandatory by using "SHALL".
NFPA Standard 22 (version 2003, the most recent I have read) addresses elevated tanks on towers or building structures, water storage tanks that are at grade or below grade, and pressure tanks. This standard has been posted before in the Forum but I am uploading my copy for you and others to download. The link is [link Point to another website Only the registered members can access]
The comments I am about to make are based on that year edition.
Chapter 13 Pipe Connections and Fittings, section 13.4 Filling, clause 13.4.1.3 states that "the bypass shall be sized to fill the tank in 8 hours". This Bypass around Check Valve is required for the filling pipe where the tank is to be filled from the fire protection system under city or fire-pump pressure.
And clause 13.4.2.1 requires that "when the tank is to be filled by a special filling pump, the pump and connections shall be of such size that the tank can be filled in 8 hours".
It can be seen that both cases are 8 hours, in agreement with the Guidelines for Fire Protection book.
When you get to browse NFPA 22, you will come across section 7.2.9 Water Filling Supply, clause 7.2.9.1 which indicates that "the filling supply or pump shall be reliable and shall be capable of replenishing the water that is required to be maintained in the tank with the required air pressure restored in not more than 4 hours". I do not think that this is related to your needs given that this requirement applies to pressure tanks which shall be permitted to be used for limited private fire protection services, such as those covered by the following NFPA standards:
(1) NFPA 13, Standard for the Installation of Sprinkler Systems
(2) NFPA 14, Standard for the Installation of Standpipe and Hose Systems
(3) NFPA 15, Standard for Water Spray Fixed Systems for Fire Protection
And pressure tanks shall not be used for any other purpose.
Finally, many years ago I read some guidelines of the INDUSTRIAL RISK INSURERS related to fire protection design. I recall that there was a requirement for replenishing the firewater spent at a rate of 50% the design discharge rate of the system, the worst case scenario discharge rate. Sorry I can not give you more details. I know I had a copy but I could not find it. That is why i took me some time to give you a hand.
I hope I could help you and I invite other members to make comments.
Regards