    Standard signal in fields Current and Pneumatic

    It would be highly appreciated if some one could let me know these questions regarding the signals.
    Why we use 3-15 psi why not other limits i.e 0-15 psi or any other values other then this?
    Why we use 4-20 mA why not other values i.e 0-20 mA any other values other then this?

    Regards,

  2. # ADS
    Spons Circuit
    Join Date
    Always
    Location
    Advertising world
    Posts
    Many
     
  3. #2

    Join Date
    Sep 2008
    Location
    Here only- EGPET
    Posts
    699
    Blog Entries
    5
    I think you are not from instrument field,

    1) 3 requires for differentiate live zero and dead zero (instrument fail), 15 requires to maintain linearity with flapper nozzle design. Also you can find other signals as 3 to 30 psi, 3 to 50 psi in rare cases for specially designed instruments.

    2) same way for 4 ma requires for live and dead zero differentiate, 20 ma and 4 ma combination requires to convert to voltage through 250 ohm std. rasister linearly to 1 to 5 v dc. Above 25 ma as per biomedical laws a human can get shock( internal to body cell) with 24 vDC. there are some instrument which have option of 0 to 20 ma span of measurement.
    Last edited by amshah; 07-08-2010 at 11:35 AM.

  4.    Sponsored Links



    -

  5. #3

    Join Date
    Mar 2009
    Location
    pakistan
    Posts
    3
    Blog Entries
    3
    well sir i am from instrument field

    well i know that we need to keep the circuit thts y we use 3-15 psi and 4-20 ma but the question is y this y not 1-15 psi or 2-15 psi psi or otherwise and same case with 4-20 mA y we do not use 1-20 mA y do we have to use 250 Ohms resistance we can have a resistance of higher range and is it coz of the 1-5 v requirement of the cards? what if we use lower limits of 1-4 V?

  6. #4
    Perhaps the link below will help you

    [link Point to another website Only the registered members can access]


  7. #5

    Join Date
    Sep 2008
    Location
    Here only- EGPET
    Posts
    699
    Blog Entries
    5
    Based on my erlier reply and begas link, i would like to summurise here, if not correct- please correct

    1) pneumatic : 3-15 psi- signal starts other then zero is for live and dead zero, 3 to 15 psi is meant for linear response of the flapper nozzle design in this region.

    2) 4-20ma : above zero requires for live and dead zero, in europe still it is 0 to 20 ma.

    4 to 20 is requires to convert the same to 1 to 5 volt which normally can be measured at receiver side very easily with standard highily (.0005%) accurate 250 ohm resistor. If it is 4 to 21 or other values, non standard resistor is requied to manufacture which is difficult to get from open market and there (may be) a std. for resister values.
    and above 25 mA shock hazards remains to human cell.

    Hope it meets your requirement.

    Nice point for discussion : to refresh basics
    Last edited by amshah; 07-09-2010 at 07:17 AM.

  8.    Spons.


  •   

Similar Threads

  1. IEC standard current ratings
    By bilalqasim in forum Electrical & Power Engineering
    Replies: 0
    Last Post: 07-31-2013, 09:45 AM
  2. Pneumatic Conveying
    By johnexxon in forum Pipeline And Fluid Flow
    Replies: 0
    Last Post: 06-12-2013, 07:03 PM
  3. [request] iso standard for pneumatic fluid power
    By arifinbc in forum Pipeline And Fluid Flow
    Replies: 0
    Last Post: 12-02-2012, 04:46 PM
  4. pneumatic test for gas pipeline
    By rudiawan in forum Pipeline And Fluid Flow
    Replies: 0
    Last Post: 05-08-2010, 04:02 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •