Thread: ask for make-up time to refill fire water tanks

  1. thank you

  2. # ADS
    Spons Circuit
    Join Date
    Always
    Posts
    Many
     
  3. #14
    VdS CEA 4001 if someone ask:
    not less then 36 hours, no matter what fire hazard.

    "8.3.3 Zulaufraten für Vorratsbeh&auml;lter
    Die Wasserquelle mu&szlig; in der Lage sein, den Vorratsbeh&auml;lter innerhalb von
    36 Stunden wieder aufzufüllen."

    Regards
    zaconja

  4.    Sponsored Links



    -

  5. #15
    Hi zaconja:

    Thanks for your post. Just one comment and please correct me if I'm wrong.

    Instead of saying "not less than 36 hours, no matter what fire hazard", I guess it should state the opposite; that is "not more than 36 hours, no matter what fire hazard". Otherwise, it would mean that it is prohibited to replenish the supply in less that 36 hours and there is no upper limit (e.g. one week would be OK).

    Regards
    ..

  6. #16
    Quote Originally Posted by f81aa View Post
    Hi zaconja:

    Thanks for your post. Just one comment and please correct me if I'm wrong.

    Instead of saying "not less than 36 hours, no matter what fire hazard", I guess it should state the opposite; that is "not more than 36 hours, no matter what fire hazard". Otherwise, it would mean that it is prohibited to replenish the supply in less that 36 hours and there is no upper limit (e.g. one week would be OK).

    Regards
    Yes, my fault, I wrote one thing, thinking about other things ....
    No longer than 36 hours is correct.
    ragards,
    zaconja

  7. #17
    related to the water tank for fire fighting in hotels, can also be used water from a large swimming pool?
    Not from the pool that serves to compensate for water in large pools, rather than just from a large pool where guests can swim?

    Is there someone in the group experience with common containers of water for sprinklers and outdoor hydrant network?
    Eg. for the case when a fire pump should work for sprinkler and hydrant network? Must be mounted relief valve for pressure reducing, only for the indoor hydrant network, which consumes a small amount of water?

    regards,
    zaconja

  8.    Spons.


  9. #18
    Hi zaconja:

    What do you mean by common containers of water for sprinklers and outdoor hydrant network?

    Regards
    ..

  10. #19
    in the engineering design for process safety(CCPS),secrtion 16.3.3 fire water supplies,"the onsite dedicated fire water storage should have the capability of replenishment within 24 hours." I think this requirement is reasonable.

  11. #20
    but if the plant water & fire water are supplied through a common pipeline, in my opinion,the fire water replenishment time shall not be the decisive factor to design a pipeline.the design capacity of the pipeline shall be decided by the plant water for production,rather than that of fire water.

  12. Re: ask for make-up time to refill fire water tanks

    Quote Originally Posted by taoxianwen123 View Post
    everybody,I want to ask how long it required to refill the fire water tanks after a fire in oil & gas separation plants,and which standard can I find the requirement of make-up time?
    In chinese standards, the fire water make-up time is not longer than 96h in oil & gas separation plants, and not longer than 48h in oil refineries,but I can not find the requirements in international standard.can somebody tell me?
    To be frank it depends on the filling capacity of the machinery. In most cases it can be early also or it may take more than 96 hrs also.

Similar Threads

  1. Tanks Fire and Safety Design
    By ivan_s60 in forum Safety And Environment
    Replies: 6
    Last Post: 09-04-2014, 05:11 PM
  2. Fire fighting fire water pump design
    By aniket00786 in forum Safety And Environment
    Replies: 1
    Last Post: 06-13-2014, 07:31 AM
  3. Replies: 0
    Last Post: 08-05-2010, 02:23 PM
  4. Article: ask for make-up time to refill fire water tanks
    By taoxianwen123 in forum Home Articles
    Replies: 0
    Last Post: 08-05-2010, 02:16 PM
  5. ask for the make-up time of fire water?
    By taoxianwen123 in forum Safety And Environment
    Replies: 0
    Last Post: 07-29-2010, 08:52 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40