Quote Originally Posted by surgeArrester View Post
You can always change the PF at the rating tab, where you can see the "table" for the MW, PF and others. That is where you will set the appropriate setting, always make sure it is also reflected in the LF study case.



same in no. 1, but still, you need to have 1 generator as swing, for the sharing, you will set the other generator for their loading, the swing generator will absorb all other excess of the other generator, if the swing generator loading is in excess to its rating, it will say over loaded, so change the other of the other generator, you will set the kW sharing of these generators.

Example, Setting 2 generators as swing will divide the total loads into 2 equal loads for the generator. If one swing and other voltage, you can set the other generator on how to be loaded, the swing generator will adjust. But sometimes it will be overloaded, so adjust the other generators that the swing generator will not be overloaded.

remember we are only talking of the steady state loading.



I dont have easy power, if you are willing to share it with me, I will be willing to help you. Of which i think would be difficult on your part.. hehe..



Hope you had good technical feedback from me.
Thank you for the valuable feedback.
As far as my research on going, other SW still is using PQ and PV concept which is equivalent.( cant remember which website I read about it).