Originally Posted by
Rudi Tua
Hi Saberetap,
It is not easy for me to understand your question, but hope this can help
1. ANSI 50 you mean instant OC?, yes of course, as far as the coordination is perfect
2. The time delay 0.15s is not ANSI 50 behavior, please use 51 if you want to add any delays more than milli second, especially (for me) about 2 second delay is suicide for the generator or other electrical equipment.
3. About function 50 and 67, it depends on the relay type you use, if you choose the digital relays (exp. GE UR relay) than you can use only 1 relay onboard and also in ETAP file
4. Setting 59 and 67 ... well, setting for me is an "art", once again, depends on the system itself and the art of the engineer. eventhough there is some rule of thumb for it.
Hope that help you.
Thanks