The short circuit apparent power is for the symetrical three-phase fault for your circuit --> S= 1500 MVA . It´s a net parameter, independient of the fault type.
The first expression for the symetrical short citcuit current is OK.
Ik3''=(c*Un)/(sqrt(3)*|z(1)|) or as you noted, according to IEC 60909
For a line to ground fault the expresion is (for symetric components):
Ik1''=(sqrt(3)*c*Un)/|Z(1)+Z(2)+Z(0)| according to IEC 60909, if the fault is far-from generator Z(1)=Z(2), and the Z(0) is function of the earth system.
If you choose a value for Z(0)=200 ohms for overhead lines and Z(0)= 60ohms for an underground network. Normally, the electric company limit the zero sequence current to 300A or 1000A respectively, to avoid dangerous step and touch voltage to people.





Reply With Quote