Results 1 to 7 of 7
Thread: earthing calculation
  1. earthing calculation
    Hi all,
    Currently i'm doing earthing calculation based on BS 7430. our plant has limited area, only 18m x 22m. soil resistivity is 244 ohm-meter.
    according user requirement, resistance shall be max 4 ohm.
    after calculate with the hollow square, 9 rods, i just got 5,565 ohms.
    please advise how to get resistance below 4 ohms?
    your response is highly appreciated.
    thank you
  2. Re: earthing calculation
    Hi All,
    do you ever try to combine hollow square and line configuration?
    please share if you have experience on this.
    thank you
  4. Re: earthing calculation
    Hi All,
    thank you
    I did a simulation with your parameters received 5,67Ohms, for 8pcs of 3m copper bound steel rods, in hollow square configuration, after adding another cross-connection copper wire (all wire with 10mm dia., around 150mm2).
    I tried double square configuration, keep squares 3m distance one from another (square in square), add more rods, total 15. Still, resistance too high : 5.29Ohms.
    You need to improve earth with the active electrodes (with salt), etc, which is beyond our calc, and should be done by supplier of such electrodes.
    Cheers
    Cheers
  8. Re: earthing calculation
    Thank for your response.
    please see below picture for my configuration.
    my calculation :
    R=ρ/2πL [log_e [8L/d]-1]
    Where
    R : the resistance of rod or pipe, in ohms (Ω)
    L : the length of the rod or pipe, in meters (m) = 15 m
    d : the diameter of the rod or pipe, in meters (m) = 0.0603 m
    ρ : the soil resistivity in ohm meters (Ω-m) = 244 ohm-m
    Substituting the values.
    R=244/(2Ï€×15) [log_e [(8×15)/0.0603]-1]
    R=2.5889 [7.5959-1] Ω
    R=17.076 Ω
    According to BS 7430, Resistance of vertical parallel:
    R_n=R[(1+λa)/n] => a=ρ/2πRs
    Where
    Rn : the resistance of multiple electrodes
    R : the resistance of one electrode in isolation, in ohms (Ω) = 17.076 Ω
    s : the distance between rods, in meters (m) = 8.25 m
    ρ : is the resistivity of the soil, in ohm meters (Ω-m) = 244 Ω-m
    λ : A factor for electrodes
    : an hollow square = 7.65 (refer to BS 7430 table 2)
    : parallel in a line = 1.66 (refer to BS 7430 table 4)
    n : no. of electrodes arrange
    The resistance of rod electrodes in hollow square R1:
    a=244/(2×Ï€×17.076×8.25)
    a=0.252686
    R1=17.076[(1+7.65×0.275657)/9]
    R1=5.898 ohm
    please whether my calculation is correct or not.
    actually in BS7430:2011 page 93, give an example for combination between hollow square and line configuration to reduce the resistance. but i'm still not sure since some value of variables are wrong.
    any suggestion?
    thank you
  9. Re: earthing calculation
    my calculation :
    Where
    R=244/(2π×15) [log_e [(8×15)/0.0603]-1]
    R=17.076 Ω
    Where
    a=244/(2×π×17.076×8.25)
    a=0.252686
    R1=5.898 ohm
    any suggestion?
    thank you
  1. what is the calculation procedure for sizing of earthing busbars?
    By gilbertomejiac in forum Electrical & Power Engineering
    Last Post: 05-30-2014, 03:02 AM
  2. Earthing and Neutral
    By josemi.rodriguez in forum Electrical & Power Engineering
    Last Post: 11-20-2013, 11:45 AM
  3. Earthing transformer in ETAP?
    By popy in forum Electrical & Power Engineering
    Last Post: 07-17-2013, 09:38 AM
  4. electronic earthing
    By sridhar in forum Instrumentation & Control
    Last Post: 06-29-2013, 08:17 AM
  5. earthing calculation for plant as per IEE
    By saraswatapalit in forum Electrical & Power Engineering
    Last Post: 06-09-2013, 09:21 AM