    The above reference "Tank_Linings_for_Chemical_Process_Industries" is unlikely to be suitable for fuel as it is for rubber linings. Petrol, diesel and Jet A-1 (kerosene) storage tanks, if to be lined are lined with an epoxy coating, and Jotun will make one. The epoxy should not (a) deteriorate in contact with petroleum fuels; and (b) affect the fuel that is being stored. The paint manufacturer should state this on his data sheet. In the case of Jet A-1 it is usual to ask the paint manufacturer of evidence that the internal coating has been tested and approved by a major international oil company. Sometimes it says this on the data sheets.

    Externally the coating is different, (one of the reasons being that epoxy deteriorates in sunlight.

    Often petrol and diesel storage tanks are not lined at all on the inside, but can be. Often the floor only with the first 500 mm up the wall only is lined. For Jet A-1 the floor at least should be lined. Lining allows the corrosion allowance to be reduced or a situation that is borderline according to API 653 to be arrested.

    External coating is traditionally a three coat system, namely inorganic zinc / epoxy / polyurethane (acrylic modified). The inorganic zinc is suited to a shop applied system (needs abrasive blast preparation, can require moisture to cure), and so epoxy zinc can be substituted instead. The epoxy can have a miscellaneous filler, or MIO (micaceous iron oxide) or glass flake, depending on the weather exposure and price. MIO can also be the top coat (even though epoxy), if a grey colour is acceptable). Another alternative is to have a polysiloxane system (polysiloxane can be epoxy modified - PPG brand, or acrylic modified - International brand). A left field is a water bourne inorganic zinc and overcoat with water bourne acrylic (requires blast surface to start with). With the polysiloxane versus traditional urethane, the polysiloxane is more expensive, but the manufacturer may be able to design a two coat system rather than three coat system, saving labour. Coating choice may depend on coating application method, eg blast versus roller, encapsulating the tank to capture spray drift and/or quick drying selection.

    If the tanks have an existing external coating on them and sound coating is to remain, then the answer may be different.

    Manufacturers can be Jotun, International, PPG, for example.

    Jiminy

  4.    Sponsored Links



    -

  5. #15

    Join Date
    Apr 2011
    Posts
    1
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Enilson, podrias enviarme una copia, por favor. Gracias
    marcant622@yahoo.com. Gracias Ednilson

Similar Threads

  1. API Petroleum Storage Tank Design
    By surendra.bhatkar in forum Safety And Environment
    Replies: 3
    Last Post: 02-05-2014, 09:12 AM
  2. Article: Coating in storage tank
    By sumon emam in forum Home Articles
    Replies: 0
    Last Post: 03-23-2011, 09:43 AM
  3. Coating in storage tank
    By sumon emam in forum Petroleum Refining
    Replies: 3
    Last Post: 03-22-2011, 01:26 AM
  4. Article: Coating in storage tank
    By sumon emam in forum Home Articles
    Replies: 0
    Last Post: 01-22-2011, 12:52 PM
  5. Coating in Petroleum storage tank
    By sumon emam in forum Petroleum Refining
    Replies: 0
    Last Post: 01-18-2011, 05:05 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •