    Tank Venting Calculations

    hello,everybody:
    how to select the wetted surface of a low-pressure storage tank when itself catches a fire rather than it is exposed to a pool fire ?
    when we calculate the fire water demand or tank breathing valve's venting capacity of a low-pressure storage tank with PV valves on the roof,we will decide the wetted surface of the tank.but in all of the standards or handbook,such as API RP 521,API 2000,they say:the up-limit of the wetted surface normally is 25 feet(required in API RP 521-1999 clause 3.15), or 30 feet(required in API 2000) ,the part which is higher than that up-limit may not be protected or may be not calculated when calculating the breathing valve's venting capacity.All of the up-limits are based on the assumption that the tank are exposed to an outside fire or pool fire,the pool fire's flame can not impinge higher than that up-limit.
    We ignore the conflict of the value(25 or 30 feet) of different standards,we talk about why all of the standards consider the up-limit based on the assumption that the tank are exposed to an outside fire or pool fire(it means to calculate the venting capacity of adjacent tank rather than buring tank)?why not consider the burning tank itself?if a low-pressure storage tank catches a fire at its low-low level,and this tank's height is higher than 30 feet ,how to select its wetted surface when calculating breathing valve's venting capacity?
    in API 2000,table 3B footnote a,it says"Engineering judgment is to be used in evaluating the portion of the area exposed to fire."
    so,for the buring tank,the whole tank height shall be considered.
    but,why all of the standards consider the tank venting capacity based on the assumption of exposing to a pool fire?why not consider the buring tanks' venting?

  2. # ADS
    Spons Circuit
    Join Date
    Always
    Posts
    Many
     
  3. There is no conflict between API 521 and 2000, API 521 is not applicable to storage tanks.

    How could a storage tank catch fire and would venting actually still matter?

    Btw, both API standards you are referring to have been replaced / updated. They're now ISO standards as well.

  4.    Sponsored Links



    -

  5. #3
    thanks Nephilim .
    but do you know the ISO standard name and code No. for tank venting?

  6. Quote Originally Posted by taoxianwen123 View Post
    thanks Nephilim .
    but do you know the ISO standard name and code No. for tank venting?
    ISO 28300 "Venting of Atmospheric and Low-Pressure Storage Tanks"

  7. #5
    thanks a lot.

  8.    Spons.


  9. #6
    API Standard 2000 6th Ed. Nov. 2009 - Venting Atmospheric and Low-Pressure Storage Tanks - ISO 28300;2008.pdf

    [link Point to another website Only the registered members can access]


  10. #7
    ISO 28300 1st Ed. 2008 - Petroleum, petrochemical and natural gas industries — Venting of atmospheric and low-pressure storage tanks.pdf

    [link Point to another website Only the registered members can access]


  11. #8
    thnx nabilia

  12. #9
    Nabilia, thanks for your posts #6 and 7.
    ..

  13. #10
    in NFPA FIRE PROTECTION HANDBOOK(19th edition),page 6-302 says:
    The required flow rate permitted by NFPA 30 to be multiplied
    by an appropriate factor F listed in the following schedule
    when protection is provided as indicated (only one factor may be
    used for any one tank):
    • 0.5 for approved drainage for tanks over 200 sq ft (18.6 m2)
    of wetted area
    • 0.3 for approved water spray and drainage
    • 0.3 for approved insulation
    • 0.15 for approved water spray with approved insulation and
    drainage
    With some restrictions, the above factors may be reduced
    by 50 percent for liquids with heats of combustion and rates of
    burning equal to or less than those of ethyl alcohol (ethanol), but
    in no case can the factors be reduced to less than 0.15. See
    NFPA 30.
    but all of the vent capacity is based on the assumption that the tank is exposed to a outside fire, how to calculate the vent capacity or venting flowrate of buring tank?

  14. #11
    correct:how to calculate the vent capacity or venting flowrate of burning tank?

  15.    Spons.


  16. thanks

  •   

Similar Threads

  1. Tank Calculations API 650
    By praphulla.phirke in forum Engineering Spreadsheets & Presentations
    Replies: 246
    Last Post: 01-15-2019, 01:16 PM
  2. Tank Calculations API 650
    By praphulla.phirke in forum Mechanical Engineering
    Replies: 232
    Last Post: 08-25-2015, 11:02 AM
  3. Article: Tank Venting Calculations
    By taoxianwen123 in forum Home Articles
    Replies: 0
    Last Post: 05-02-2011, 10:52 PM
  4. Article: Tank Venting Calculations
    By taoxianwen123 in forum Home Articles
    Replies: 0
    Last Post: 12-03-2010, 08:19 PM
  5. Article: Tank Venting Calculations
    By taoxianwen123 in forum Home Articles
    Replies: 3
    Last Post: 11-12-2010, 10:36 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •