  1. condenser water box top elevation

    can any one tell me why is it desirable to have condenser elevation in a power plant higher than that of cooling tower inlet. As mentioned above cooling water head will be governed by condenser top.

  2. #2

    Re: condenser water box top elevation

    The condenser w&#225;ter box highest point should be lower than cooling tower riser to avoid vacuum when a circulating w&#225;ter pump trip.

    Otherwise additional equipment such as priming systems are required
    My recomendation is to have the condenser as low as posible , although steam turbine limits the condenser elevation

  3.    Sponsored Links



    -

  4. Re: condenser water box top elevation

    do u have any condenser design guide