    Question Modeling explosion in PHAST 6.54

    Hi
    I would modeling explosion in PHAST
    How i can calculate "confined volume"?

    thanks

  2. The Following User Says Thank You to nmerzak For This Useful Post:

    rokan123 (10-06-2013)

  3. # ADS
    Spons Circuit advertisement
    Join Date
    Always
    Posts
    Many
     
  4. #2

    Join Date
    Jul 2010
    Posts
    102
    Thanks
    1
    Thanked 21 Times in 16 Posts
    Quote Originally Posted by nmerzak View Post
    Hi
    I would modeling explosion in PHAST
    How i can calculate "confined volume"?
    thanks
    first you should identify the areas in your plant where confinement may occur e.g. by the presence of parallel planes* barriers* physical obstructions to ventilation. These may be the air coolers* heavy loaded piperacks* elevated platforms* etc...

    Then* a guidance of the fraction of flammable cloud to be considered as "confined" to give explosion can be found in the CPR 14E "methods for calculation of physical effects" (yellow book)

    There are link somewhere in this forum where you can take this book.

  5.    Sponsored Links



    -

  6. #3

    Join Date
    Feb 2011
    Posts
    16
    Thanks
    0
    Thanked 2 Times in 2 Posts
    deep thanks safetyuser
    the broblem is:
    there is a leak in compressor station
    if i take total volume "the building volume of the compresssor station"
    how i can calculate
    1/ confined volume
    2/flammable mass in the cloud

  7. The Following User Says Thank You to nmerzak For This Useful Post:

    janedperw (06-19-2015)

  8. #4

    Join Date
    Jul 2010
    Posts
    102
    Thanks
    1
    Thanked 21 Times in 16 Posts
    Quote Originally Posted by nmerzak View Post
    "the building volume of the compresssor station"
    how i can calculate
    1/ confined volume
    2/flammable mass in the cloud
    Well* I don't know exactly your problem anyway from your few words I can suppose:
    1- confinement is 100% if your compressor is totally enclosed in a building/box-shaped shelter and similar
    2- the flammable volume in the cloud may be estimated in the worst case as the Upper Flammable Limit (UFL) of the congested gas* times the total confined volume. Use the gas density to turn into mass.

  9. The Following User Says Thank You to safetyuser For This Useful Post:

    janedperw (06-19-2015)

  10. #5

    Join Date
    Aug 2010
    Posts
    6
    Thanks
    0
    Thanked 3 Times in 2 Posts
    Quote Originally Posted by safetyuser View Post
    2- the flammable volume in the cloud may be estimated in the worst case as the Upper Flammable Limit (UFL) of the congested gas* times the total confined volume. Use the gas density to turn into mass.
    It would be more correctly to use the difference between UFL and LFL.

  11. The Following User Says Thank You to Dushmen For This Useful Post:

    janedperw (06-19-2015)

  12. #6

    Join Date
    Feb 2011
    Posts
    16
    Thanks
    0
    Thanked 2 Times in 2 Posts
    thanks for all
    for worst case we can use :
    confined volume =9*5 % total volume confinned
    total volume confinned=total volume of building-volume obsructin if exist.
    "9*5% total volume confinned" for a stoichiometric combustion.

  13. #7

    Join Date
    Oct 2007
    Posts
    24
    Thanks
    0
    Thanked 1 Time in 1 Post
    Check Chapter 17 of LOSS PREVENTION IN PROCESS INDUSTRIES - LEE VOLUME 2* It may help you. Book is availabe in the forum.

  14. #8

    Join Date
    Nov 2008
    Posts
    2
    Thanks
    0
    Thanked 1 Time in 1 Post

    Explosion Modelling

    I understand from the discussion that you are trying to use the MultiEnergy model in Phast.

    PHAST needs 3 inputs for VCE* flammable mass* confined volume and blast strength.

    However in PHAST once you determine the confined volume* it considers that the entire confined volume is filled with stochiometric concentration and is available for explosion. Thus put flammable mass as say 1000kg. ( Otherwise based on the volume calculate the stochiometric flammable mass* but you will get the same results at the end * so as long as you are putting any value greater than stochiometric mass results are same).

    Identify the confined area within the plant* the congested volume is typically the volume of the congestion minus the volume of the equipment located within the congestion. e.g. if there is a structure supporting 2-3 process equipment* then confined volume is structure volume ( L*B*H) - VOlume of the process equiment. ( Explosion happens due to flame acceleration i.e. due to congestion* flammable gas cloud from any source can lead to flammable gas to reside within the congested area. Assuming entire congested volume as described is worse case but widely used in Industry )

    For the blast strength* use Kinsella method available in Yellow Book. DOnt use too much coservative values without any basis as the resultant peak overpressure will be much higer.

    If you need any further help* you can contact me on

    rajkumarlodha@hotmail.com

  15. The Following User Says Thank You to raj_lodha1 For This Useful Post:

    noiha (03-04-2013)

  16. #9

    Join Date
    Nov 2011
    Posts
    7
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Averaging-Time

    Please i need help

    i don't understand the concept related the Averaging-Time . Could someone provide me basic documentary tools.
    I tried some books (too specialisied) but i find it difficult to understand.
    tHANKS

  17. #10

    Join Date
    Oct 2007
    Posts
    24
    Thanks
    0
    Thanked 1 Time in 1 Post
    Hello*
    Can we model dust explosion scenarion in phast.
    What i have done*
    Converted mass of sulphur to TNT equivalence mass and used TNTmodel. Have anybody tried this earlier?????

  18. #11

    Join Date
    Aug 2010
    Posts
    6
    Thanks
    0
    Thanked 3 Times in 2 Posts
    Using TNT equivalence for dust explosion is not a good idea for 2 reasons (you are trying to use some correlations with VCE* for which TNT equivalence method widely applicable):
    1) mechanism of burning of dust and vapor is very different - for dust explosion you may see up to 8 explosions for same mixture (coal* for example) - relay mechanism. As a result of this* dynamic of pressure generation and its max value for dust exp. and VCE are different.
    2) you have no correlations for calculation of flammable mass of dust* because in different conditions the difference between flammable mass of dust in the same dust cloud may be up to 10 times.

  19. The Following 2 Users Say Thank You to Dushmen For This Useful Post:

    f81aa (01-08-2012), noiha (03-04-2013)

  20. #12

    Join Date
    Jul 2012
    Posts
    12
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Re: Modeling explosion in PHAST 6.54

    please give the link if anybody having PHAST software ......

Similar Threads

  1. Explosion at BP Refinery
    By Mohamed in forum Safety And Environment
    Replies: 2
    Last Post: 12-09-2011, 01:34 PM
  2. about phast discharge modeling!!!!!!
    By driftshade in forum Safety And Environment
    Replies: 4
    Last Post: 08-23-2010, 02:50 PM
  3. Article: about phast discharge modeling!!!!!!
    By driftshade in forum Home Articles
    Replies: 1
    Last Post: 07-30-2010, 04:27 PM
  4. Article: about phast discharge modeling!!!!!!
    By driftshade in forum Home Articles
    Replies: 0
    Last Post: 07-08-2010, 05:51 PM